Discuss light switch old wiring help in the Lighting Forum area at ElectriciansForums.net

Reaction score
2
hi could some one please help me with the wires on this light switch please i need to change it to a new one
any help would be apreciated thanks
 

Attachments

  • 370328378_1442337689882030_6252698600427745756_n.jpg
    111.4 KB · Views: 16
  • 370312838_1470876373678780_3145677010895777353_n.jpg
    103.1 KB · Views: 16
Are there terminal markings at the switch for the red, yellow and blue wires?
Is there earth wires attached to the back box?
 
Is there any marking moulded into old switch?

I would think the one switch with red, blue, yellow… put the red into Com, and the yellow/ blue into L1 and L2 of the new switch.

On the other half, one red into Com, other red in L1 or L2… doesn’t matter which.

The new switch is simply 2 separate switches on the same plate.

IMG_4630.jpeg
 
Are there terminal markings at the switch for the red, yellow and blue wires?
Is there earth wires attached to the back box?
hi the only marking are the middle with com and the back box are earthed i did change the one upstairs yesterday wich is a single switch were there was 2 red wires together red and yellow together and the blue on its own if that helps
 
As with the drawing above.
The red, yellow and blue wires, blue into COM, red into L1 and yellow into L2 (it is odd red isn't into COM on the old one but doesn't matter).
The two reds, one into COM the other L1, doesn't matter which way around.
You also need the earths connecting to the earth terminal on the new switch.
 
As with the drawing above.
The red, yellow and blue wires, blue into COM, red into L1 and yellow into L2 (it is odd red isn't into COM on the old one but doesn't matter).
The two reds, one into COM the other L1, doesn't matter which way around.
You also need the earths connecting to the earth terminal on the new switch.
thanks very much for taking time out to help it worked a treat much apreciated
 
ok, i assumed red was in Com.

Shows how complex even simple light switch connections can get.
At least this one had a 'before' photograph taken.
I was pretty sure the centre was COM but had the blue in whereas most people would use the red.
 

Reply to light switch old wiring help in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
631
Hi Total novi e but have wired multiple light switches previously and survived :) I've bought a nice WiFi enabled dinner switch for a new LED...
Replies
11
Views
964
Hi can anyone help me with this light switch? Photos of how it was wired to old switch but new switch is different with different names. I’m...
Replies
2
Views
1K
Hello, I’m trying to change a pendent light, I’ve wired it the same as the previous light that was on there however the light is now permanently...
Replies
27
Views
2K
Hi, I have a 220v House I want to change this switch to smart switch, but I am stumped, I don't have a neutral so I had to return the switch I...
Replies
2
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock