Discuss Lighting circuits are not earthed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
39
hi all, yesterday I went to carry out an EICR on a 1 Bedroom Flat. The lighting circuits are not earthed,the installation is about 40 years old.
The only thing I can do is C2 would you agree?
It has RCD protection.
It has some class 1 fittings.
 
So if he changes the class 1 fittings to class 2 it would be a C3? Would a label on the cu warning that the lighting circuits are not earthed and not to fit class 1 fittings work?
The client would not be happy to rewire the lighting circuits.
Further more it has been like it is for 40 years.
A rewire would be a hard sell
 
So if he changes the class 1 fittings to class 2 it would be a C3? Would a label on the cu warning that the lighting circuits are not earthed and not to fit class 1 fittings work?
The client would not be happy to rewire the lighting circuits.
Further more it has been like it is for 40 years.
A rewire would be a hard sell

Yes if all done above C3.
You could go a little further and fit nylon machine screws or get some accessories that have plastic screw covers.
 
The wiring will be more than 50 years old at the youngest as the requirement for cpcs in lighting circuits came in 1966.

C2 as is, rewiring should be strongly recommended. Do the switch drops have conduit to pull down ? They often do at that age.
 
If metal back boxes and metal screw lugs with no caps id still be C2ing it even after doing away with class I fittings. This is also the guidance given by napit so you could also check with your scheme if your with one.

First and foremost you put yourself first with an EICR. You need to be able to sleep at night, the client not wanting to spend money if it is so required is no concern of yours, just leave him with an unsatisfactory report if needs be.
 

Reply to Lighting circuits are not earthed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
419
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
I trained as a electrician in the 70s but have long since retired. Just had an EICR test done on my property in advance of selling. I have a 60s...
Replies
25
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock