B

Bill avoider

:welcome::conehead:Why are capacitor used across the contacts of lighting control contactors. I had some trouble with fluorescent lights blinking and found 48 volts coming thru the cap.277 volt circuit. Removed the cap and blinking stopped
 
Capacitors are used as a snubber to reduce arcing of the contactor contacts.
I think you might have a bit of a serious issue if the lights are flickering and you've got 277V on the circuit,

was that 277V L-E or L-N?
 
He's in the US, 277V is used for commercial lighting. The suppression capacitor was probably passing enough reactive current to charge the capacitors in the ballast up to the point that the tube would strike and discharge them.
 
yes usa 277 for most commercial lighting. so the capacitors are to help limit arching and have nothing to do with power factor correction? I was reading 48 volts passing thru, enough to flicker the lamps. any harm in removing the caps ? thanks for your help
 
never mind the caps. as you're in Pa, can you get me a few zippos cheap? :rolleyes4:
 

Reply to Lighting contactor with capacitor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
746
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
626
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock