Search for tools and product advice,

Discuss Link between N - CPC on fluorescent... what is it? in the UK Electrical Forum area at ElectriciansForums.net

NDG Elecs

-
Esteemed
Arms
Reaction score
1,751
DSC_1304.jpg

Hello folks,

I hope the picture shows ok. If it does not show, then basically there is a blue disc approx 25mm in diameter that may have a resistor or something in it. It is approx 4mm ' thick'.

The blue disc is linking between neutral and earth on the fitting. Never noticed these before and the casing of the fitting is live when energised, which is not good!

Fluorescent's puzzle me at the best of times!

Thanks.
 
i'd have expected that to be across L and N. and what means are you using to determine that the casing is live?
 
Thanks Daz,

Can these be omitted. Only one fitting out of five in total had it in. And didn't have time to check thoroughly but it may be causing a N-E fault.

Thanks
 
Agree with tel above, should be across L & N like capacitor for PF correction...maybe its a dummy load "thingy" usually installed for some makes of PIR switch although should still be between L&N.

load "thing" = load capacitor
 
Last edited by a moderator:
Cheers Tel, bit short on time so will get back to you later but was initially doing an R2 to the fittings and all CPCs were open cct. Bit puzzled as this cct rewired 4 years ago. Found the problem at switch where no continuity between CPCs. Anyway, when the lights were on I touched the casing and got a tingle. So tested with mft and a fluke t5 between MET and the casing. Got 230v both times.

Thanks
 
At the top of the picture it looks like your earth is not connected.
The capacitor is a transient voltage arrestor (cheap fittings).
If your fitting is showing live at all times then you need to check polarity, even as far back as the meter.
So, no earth, capacitor across live (blue wire) and case.
Boydy
 
At the top of the picture it looks like your earth is not connected.
The capacitor is a transient voltage arrestor (cheap fittings).
If your fitting is showing live at all times then you need to check polarity, even as far back as the meter.
So, no earth, capacitor across live (blue wire) and case.
Boydy
it is connected...the earth tag is at the bottom of the connector block...as is the twin`s CPC...
 
top of pic is missing. looks like some connectable has been done.ion/extension of c
 
It is as stated earlier a surge suppressor, but it has been install incorrectly. Should be across L & N. Only really used to protect sensitive electronic equipment, such as alarms and psu`s....wont do any harm removing it from a fluorescent fitting.
 
Hi,

Maybe my eyesight, but is that a brown ( live ) cable connected into the Neutral terminal. Hard to determine without seeing the full picture of the fluorescent wiring, and yes; the capacitor should be L-N.

Regards.
 
Thanks for all responses folks.

The CPC is connected and the live does not go into the neutral. The other twin is looping to another florry.

The fittings are cheap and the trunking work is the worst I have ever seen. Apparently the, ahem, 'spark', ahem, that installed it disappeared midway through the rewire around four years ago.

The fitting is only live when switched.

I do recall something now from college a few years back about PF correction when I think about it.

Thanks again one and all.
 
Hi Boydy,

The install is TT with Ra of nigh on 60 ohms. Was not really expecting a PD of 230V between rod and neutral. Maybe the fault is L-CPC rather than N-CPC. Need to investigate further, though I think the client prob thinks I am spinning them a yarn as only went there to fit an extra light fitting. Now they need a new earth and RCD protection!

I left the circuit isolated and will ring them tomorrow to see whats what!

in answer to your qu I have checked some Zs's out of curiosity on other circuits, and they are all around 20 ohms with water bond in place (no gas there). So the earth is not the best at present.... but did not check other circuits for N-CPC voltage, no.
 
Hi Boydy,

The install is TT with Ra of nigh on 60 ohms. Was not really expecting a PD of 230V between rod and neutral. Maybe the fault is L-CPC rather than N-CPC. Need to investigate further, though I think the client prob thinks I am spinning them a yarn as only went there to fit an extra light fitting. Now they need a new earth and RCD protection!

I left the circuit isolated and will ring them tomorrow to see whats what!

in answer to your qu I have checked some Zs's out of curiosity on other circuits, and they are all around 20 ohms with water bond in place (no gas there). So the earth is not the best at present.... but did not check other circuits for N-CPC voltage, no.


Let us know what you find Bud.

Boydy
 

Reply to Link between N - CPC on fluorescent... what is it? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
Hello guys, I have a small problem assigning the correct codes for some visual faults. I am still confused and looking forward to find a good...
Replies
10
Views
5K
D
Hi folks. I'm wondering if anyone can help with a lighting circuit fault I came across today that has me slightly baffled. I have a circuit...
Replies
11
Views
3K
P
Hi all. I've just had my house in France upgraded to single phase. I've bought a consumer unit as i only want a basic set up (minimal electric...
Replies
46
Views
10K
I was sent to a building as there were no lights in the lift motor room at the top... Got there, opened 2 x fluorescents and tested for voltage at...
Replies
22
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top