Hi all, looking for some advice. I have removed electric cooker, and was wondering can I use the 6mm cable to conect some double and single sockets or could I use the cable to create a ring main. Any advice would be greatly appreciated.
 
I think he means extending the existing, redundant circuit to some sockets. Not reuse the cable as such.
 
The 6mm could be used to feed a contactor or isolator and a ring final installed from this.
In essence it would be a hybrid circuit.
As long as the essential testing is carried out, it’s acceptable.
 
Last edited:
Aside from the general silliness we were just looking for your level of expertise and access to test equipment so we could tailor our responses to suit. :)
 
Ok lads, by your response to my question the answer is no I can't run sockets or use as a ring main. Thanks for the advice.
Yes you can providing the relevant regulations are followed and the alterations are inspected and tested by the required means.
You could even install a radial circuit, with the 6mm being the first point on the circuit and go from there.
All as long as the relevant regulations are complied with, rcd protection etc etc.
 
Hi @Philo . You can have sockets added to this. There are a few ways to do this. I would recommend that you talk to an electrician for this though. Get a few quotes and take it from there. The advantage of an electrician doing the work is that you will get a test cert at the end.
 

Reply to Looking for advice cooker 6mm cable in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Is this ok? 32amp breaker with a 6mm wire leading to fused cooker switch. This then leads with 6mm cable to hardwire point. Can i hardwire 2 x...
Replies
11
Views
763
OLDBOY
O
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
612
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
861
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
792
I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen...
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock