Hi everone,I am new to the forum and think its brilliant,I am currently
studying for my 2394&2395 and am testing everything in sight with a
fluke 1651 multi functional tester.When i try to do a loop test on a lighting
circuit,I follow all the instuctions,but i keep getting >2000 ohms,i am obviously
doing something wrong,can anyone please advise,Thanks in advance
 
I am testing between the earth and live at the switch,on the video I have that is how it shows it to be done,but I am not getting the same results,I need to point out that in the video they are using a megger and I am using a 1651 fluke
 
does the fluke need to use 3 leads? the megger testers ( except the 1700's) use 3 leads on no trip.
 
yes,it uses 3 leads,but I have just been using the L and E,as is done in the video,also in the video they are using a megger and i am using a 1651 fluke,but wouldn't think that the make would make much difference as long as its set on the right function. It is ZI for loop impedance on the tester I have,I am trying to track down a manual for it.
 
yes,that is all ok. I wiil go through the video again and see if i have missed something,but watched it numerous times and still can't see what i am doing wrong.I will persrvere till I finally get it.
 
try using 3 leads. i don't know the flukes, but with my megger 1553, using 2 leads on no trip will throw up "trip".
 
:welcome:Are connecting you MFT to the live at the switch, or the switched live with the switch in the OFF position? do you have continuity on the cpc?
 
:welcome:Are connecting you MFT to the live at the switch, or the switched live with the switch in the OFF position? do you have continuity on the cpc? ie is it connected to earth?
 
i thought so, but was unsure as the only use i've ever had for a fluke was a doorstop.
 
How about going to the fitting and performing a 3 lead test there? That would be a more accurate measure of the circuits Zs too. Although I am unsure whether you are actually testing the circuit for any reason, or is it just to get a feel for your meter?
 
yes,it is on,I am putting the earth lead on the cpc,and the live probe on the switch live,I will try it with all 3 probes,but I wouldn't be able to do that at a light switch would i? I would have to go to the rose,and on the video which is on you tube,by routledge textbooks they are doing it at the switch with 2 probes,which is the one i am trying to do,I am thinking the 1651 fluke isn't capable to test like that.
 
yes,it is on,I am putting the earth lead on the cpc,and the live probe on the switch live,I will try it with all 3 probes,but I wouldn't be able to do that at a light switch would i? I would have to go to the rose,and on the video which is on you tube,by routledge textbooks they are doing it at the switch with 2 probes,which is the one i am trying to do,I am thinking the 1651 fluke isn't capable to test like that.


I don't use a fluke but could possibly be that the tester requires you to use the 3 leads to confirm polarity.
 
Not used a fluke myself, but I think what a couple of people have suggested is to join the N-E probes before testing, rather than only using two, although this will depend on if the circuit is RCD protected.
 
yes,I am trying to get used to the meter,maybe I am watching too many videos on you tube with different meters and expecting mine to do the same,a lot of those look (are) a lot newer than mine
 
your videos probably show a megger 1700 series. these will do no trip loop tests with 2 leads. earlier megger swon't.
 
Is there RCD protection on the circuit? If not then you should be using a 2wire high current loop test.
If there is an RCD on the circuit then you will have to use the alternative 3wire non-trip loop test.
 
tried joining the E &N and it tripped the rcd,it works fine using the 3 at the rose but I don't think it can be used at the switch,at least i know now.Thanks for the help.Greatly appreciated.
 
tried joining the E &N and it tripped the rcd,it works fine using the 3 at the rose but I don't think it can be used at the switch,at least i know now.Thanks for the help.Greatly appreciated.

Yeah, 2 lead no-trip tests are only available on newer models AFAIK. Can I ask what two leads you were using before hand? I think you may have been getting >2000 because you were using the 'L' and 'E' leads. If you are doing a two lead test (continuity etc.) on every tester I've ever used you have to use the 'L' and 'N' probes.
 
Yes fluke requires 3 leads well the one I used on my 2391 did try at the pendent or fiting using 3 leads and think you use F3 to change settings also helps using instruction manual or watch you tube video with one thats using a fluke
 
It will trip the RCD because your tester will nto do a 2 lead no-trip test. The point I'm making is, if you're doing continuity or IR, you will always need to use the L & N leads, no matter what you're testing.
 
I see,thanks,I am new to testing ,been in the electrical game since i left the army 10yrs ago,and have been going to night school,would like to do a few jobs of my own but won't till i am 100% sure i know what i am doing.i have paid for an inspect and test course in june of this year,am reading Gn 3 and Osg night and day,and follow the tester at work round like a sheep,lol.I will get there eventually,i hope.
 
I've got the same tester and yes when testing Zs on a lighting circuit you do a 3 lead test from the furthest fitting on the circuit with all switches closed/on. It will work. As previously discussed there is a F1 and F3 toggle to play about with but for what you are trying to achieve you need F1 on L-PE. I forget what F3 is for now I think it toggles Re and Ik.

The Flukes are good testers. I know the Megger leccies like criticise them but I say as long as its calibrated It must be working fine whatever the make/model.
 
hi are you testing live when you test at the switch are the lights working if yes set your tester to high current you will only need two leads red and green look at the top of your screen on left ther are circles ooo use the leads in the corresponding holes for the leads in the test meter centre hole is earth right side live make sure you get a good connection to earth and live there will be a lightning sign on the tester to show its live switch the switch if that still does not give you a reading you have no earth continuity
 

Reply to loop impedance on lighting circuit in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
758
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
658
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock