Discuss Making off in main switch in the Electrical Forum Canada area at ElectriciansForums.net

E

edrobbo8

Hi guys,

Have to make off some 95mm lugs onto an old Bill main switch, which has 160A fuses. There are 4 terminals with an M10 dome head bolt with a square shank for the 3 phases and neutral, and there are currently 2 lugs on each bolt, 1 feeding a main dis board and 1 feeding a new switch fuse that goes to a seperate control room.

We need to get a third 95mm lug on to each terminal, would it be acceptable to put two lugs on each bolt secured by a nut, then our 3rd lug onto the bolt which will sit tight up to the 1st nut, and tightened up with another nut? Hope that makes sense!

Untitled.jpg
 
No, use a tinned copper spacer between the 2[SUP]nd[/SUP] and 3[SUP]rd[/SUP] lugs. One nut then tightens the full assembly evenly.

I’ve got to ask but why are you doing this? It’s bad practice to have a switch feeding more than one supply!
 
No, use a tinned copper spacer between the 2[SUP]nd[/SUP] and 3[SUP]rd[/SUP] lugs. One nut then tightens the full assembly evenly.

I’ve got to ask but why are you doing this? It’s bad practice to have a switch feeding more than one supply!

Not best practice i agree, but no different than a main switch feeding a bus bar which in turn supplies 3 further switches...
 
Thanks for the advice. The main switch supplies one dis board, and they are building a new shed and due to the increase in load for the generator, the new building has a separate generator as back up. Our system is PV so has to bypass the generator so cannot go into the existing dis board.
 
Thanks for the advice. The main switch supplies one dis board, and they are building a new shed and due to the increase in load for the generator, the new building has a separate generator as back up. Our system is PV so has to bypass the generator so cannot go into the existing dis board.

Best practice here calls for a small Bus Bar chamber before the DB. That can then be the means of connecting the DB, the new supply to the new building and your PV system. All via there own CBs...
 
What length of cable are we talking about? Sorry I wouldn’t be happy with a set up like this at all. I’m going with E54 on this a bus-bar chamber with individual protection for each of the feeds would be way to go.

It would future proof for any further expansion.
 

Reply to Making off in main switch in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains...
Replies
11
Views
3K
Hi, I have ran a light ring off a fused spur with two lights on, each with their own switch (outside and lobby light) I want to put the outside...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock