I also note that the modern equivalent:


States 0.30 ohms for 5 second thermally adjusted max Zs. But at £140 + vat each that doesn't help much!

It's worth speaking to them again and double checking whether they gave you a thermally adjusted value, and whether it was a 5s value.
Hi, on the helpline I definitely went through all this with them so I’m sure they said that the 0.23 value was the 100%, it was also for 5 second disconnection. I might actually ring them back and double check this but I’m positive I asked for the 5sec Zs value at 100%
 
Looking at the data sheet for the newer one than 5s is very close to the point when the "instant" magnetic trip would go, so base on 800A for that on you model I would agree with @timhoward you would have your hot (100%) Zs as no worse than (230V * 0.95) / 800A = 0.273 ohms at Umin, and then your 80% for hot cables measured cold as 0.22 ohm.

In a case like this where it is tight you might also want to check how hot the cables where when you measured them (might have been done live for Zs with no cool-down) and what the realistic operating temperature is going to be based on the cable & loads for the final circuits.
 
I'd pull out the clamp meter and do some max demand head scratching.
Assessing whether 100A is actually needed would help.

I know that convincing people to spend money on things that 'work fine' is tough, but maybe the steel armour is degrading, and the Zs is higher than it was when installed. I don't suppose IR test results support this theory do they?
 
I'd pull out the clamp meter and do some max demand head scratching.
Assessing whether 100A is actually needed would help.

I know that convincing people to spend money on things that 'work fine' is tough, but maybe the steel armour is degrading, and the Zs is higher than it was when installed. I don't suppose IR test results support this theory do
I'd pull out the clamp meter and do some max demand head scratching.
Assessing whether 100A is actually needed would help.

I know that convincing people to spend money on things that 'work fine' is tough, but maybe the steel armour is degrading, and the Zs is higher than it was when installed. I don't suppose IR test results support this theory do they?
The readings and installation in general are pretty much perfect with no degradation that I can see. In any other instance you’d be jumping for joy at the readings I’m getting but as I said with a incoming ze of 0.16 and a max Zs of 0.18 I’m pretty much snookered.
 
The readings and installation in general are pretty much perfect with no degradation that I can see. In any other instance you’d be jumping for joy at the readings I’m getting but as I said with a incoming ze of 0.16 and a max Zs of 0.18 I’m pretty much snookered.
I am sceptical that 0.22/0.23 is the hot Zs value. The current Proteus data sheet has 0.3 hot for 5s, and computing from the 800A magnetic trip for the model shown above looks like 0.27 ohms, so I would think 0.22 is the cold Zs value giving you 0.06 for R1+R2 which, while difficult, is a bit better.

For the sake of argument, if it is 4C 25mm SWA then R1 = 0.727 and R2 = 2.3 ohm/km so you would be OK for about 20m. If a 16mm CPC is added at 1.15 ohm/km then 32m, etc.

The other aspect is to get a more realistic value for hot operation to cold measurement. Was it all off for a long time before you measured Zs?

Did you measure Zs on the system under normal operating conditions? If so it would already be hot, OK maybe not "max load" hot, but depending on the usage maybe not far off it. If you know the cable rating/method and what the supply max is then you can also see if the max operation is noticeable less than the 70C assumed for typical use-case.
 
Hi all,
Just off the phone with Proteus and they’ve told me there is only one Zs value for these MCCBs so they are advising that 0.23ohms is the 100% value and they didn’t think that altering the mag on it would effect this as it’s for overload.
The sub main readings I’m getting for the 4 dis boards are:
0.23
0.23
0.21
0.21
So they are bang on the max or just under the Zs rating of 0.23ohms.
Would you still code a Zs that breached the 80% value but not the 100% value as a C2? Could it be put through as a C3 with a recommendation that this is looked at again closely during the next EICR? The owner has agreed to push through upgrades for the panel board at the earliest opertunity.

Help!
 
I would find it difficult to justify a C2 given they are measuring the 100% value where that seems not to quite agree with the figures given on the MCCB (800A magnetic trip) or the value for the replacement model.

Do you have any idea of how hot the cables were when you measured those values?

What is the nominal voltage there and is it on a site with its own substation transformer?
 
Ok guys, here’s an update.
I bit the bullet and phoned the NICEIC helpline and the nice guy on the phone let me know the following.
If the installation is in use whilst the EICR is being carried out then you use the 100% max Zs values of the protective devices.
If the installation is not currently in use or hasn’t been for some time that is when you use the 80% value of the Max Zs of the protective devices to account for there being no thermal effects in place for the circuits.

This came as a great surprise to me as I had always thought that EICRs used the 80% values at all times but the advisor told me that this was a myth and that he has this conversation a lot with contractors on any given week. He referenced the areas on the restricted areas of the NICEIC website where members can find this, it’s also on the front inside cover of the NIC Test Certs and also on Pocket Guide 18.

So with the information in hand I can pass that installation without any codes or notes… WHEW!

Every day is a school day as they say.
Thanks for all of your helpful input guys, much appreciated!
 

Reply to Max Zs Coding Question 80/100% in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
789
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock