Discuss Max Zs for Bs88-2 630amp fuse in the Industrial Electricians' Talk area at ElectriciansForums.net

One little word of warning, if you are measuring your Zs very close to a transformer, you may find you get false (high) readings due to the impedance of the transformer windings. I have done a little spreadsheet that will calc the Zs at the incoming terminals of a switchboard fed by a transformer. Let me know if you would like this.
 
I agree with Andy you are probably not getting a realistic Zs. You may have to introduce a known resistance and deduct this from your reading.
 
And you think the reading is not realistic because of the transformer ? How would you recommend putting a resistance on the circuit bearing in mind it's an open occupied hotel ! Sorry I've never come across this problem and not really tested bussbar
 
And you think the reading is not realistic because of the transformer ? How would you recommend putting a resistance on the circuit bearing in mind it's an open occupied hotel ! Sorry I've never come across this problem and not really tested bussbar
Accurately measure some 1.5 singles to say 0.10 ohm. Take a Zs at the busbar with meter leads only then take another reading with your known resistance in series with one of the meter leads and then deduct the 0.10 ohm and see if it differs from the original reading. This often works if you are very close to the transformer.
 
One little word of warning, if you are measuring your Zs very close to a transformer, you may find you get false (high) readings due to the impedance of the transformer windings. I have done a little spreadsheet that will calc the Zs at the incoming terminals of a switchboard fed by a transformer. Let me know if you would like this.
Hi Andy if you could pass this on would be great
 

Reply to Max Zs for Bs88-2 630amp fuse in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
0
Views
860
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
725
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock