Discuss Maximum cable length lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Been out the domestic game for a long time, but now having to rewire my own house.

Was wondering what the maximum cable length would be for a 1.0mm lighting circuit with 100w of leds?
Is the max cable length the ‘maximum’ length of r1+r2 from conumser unit - up and down switch drops - to the furthest away light?

Any help would be Greatly appreciated.

Thanks
 
How long do you need it to be?!
Assuming a TNS earthing system with highest permitted Ze and protection by a B6 breaker using 80% OSG Max Zs values, about 119m in theory.
Volt drop also needs checking but with the load you mention it wouldn't be an issue.

Yes, R1+R2 is measured at the furthest point in the circuit which will be the furthest light fitting (which will include it's switching path).
 
How long do you need it to be?!
Assuming a TNS earthing system with highest permitted Ze and protection by a B6 breaker using 80% OSG Max Zs values, about 119m in theory.
Volt drop also needs checking but with the load you mention it wouldn't be an issue.

Yes, R1+R2 is measured at the furthest point in the circuit which will be the furthest light fitting (which will include it's switching path).
Ive basically used 100m of 1.0mm, looped the feeds at each switch then switch wire to light.
Just confused with max cable length as it’s been a while.
The 100metres includes each switch wire, hence I asked if the max cable length was from consumer unit to last light fitting (including switch drops)
Thanks again
 
And 2 way switch circuits can make a big difference (eg 3 story house with intermediates on each landing eats up the cable
and the opposite applies if you use Quinetics wireless switches for these situations, they can save a heap of cable (but are a fair price)

The 100metres includes each switch wire, hence I asked if the max cable length was from consumer unit to last light fitting (including switch drops)
It's the complete current path of the R1 including switching. As you've looped at the switches, the R1 path is from consumer unit via each switch and to the last light fitting, but not including the cable from every other switch to every other light fitting. Same for the R2 path back. So it won't be as bad as the total cable used multiplied by the resistance / meter.
 
and the opposite applies if you use Quinetics wireless switches for these situations, they can save a heap of cable (but are a fair price)


It's the complete current path of the R1 including switching. As you've looped at the switches, the R1 path is from consumer unit via each switch and to the last light fitting, but not including the cable from every other switch to every other light fitting. Same for the R2 path back. So it won't be as bad as the total cable used multiplied by the resistance / meter.
Understood. Thanks a lot for your help, much appreciated
 
Yeah, I’ve used 100metres in total.. longest run including all switch wires to the last fitting is 55metres.. that sound ok?
If your longest run is 55m including the switch circuit for the 'furthest' point then yes sounds alright as OSG states about 120m [post #] but double check it with a MFT.
 

Reply to Maximum cable length lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I was thinking to add some lights like in the attached image, basically twin batten lights to my attic but i'm not familiar with strip...
Replies
4
Views
742
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
407
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
684
Doing a rewire at the minute and was wondering if anyone has ever seen or heard of a lighting circuit being connected somewhere in an installation...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock