Discuss MEM RCD/MCB tripping during night in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
37
Hi

Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring main only - this is tripping around 3-4am every morning told me had this off and on for a year. Not connected to anything on a timer eg heating / lights..

Unplugged / switched off everything and still happening , I have checked out circuit wiring and don’t have any faults also RCD test 1/2,x1,x5 and was ok - doesn’t happen during day so not been able to simulate

Anyone had this or wondering if some issue with older breaker / maybe voltage changes during night or something not thought off or just change our consumer unit and do more testing on wiring with all fully disconnected
 
My first thought was point 2 as well, given issues with MEM and smart meters posted on here before.
Hi cheers hadn’t seen about smart meters and MEM & there was one right next to CU will take a look through the forums

Will try ramp test as well actually annoyed I didn’t do that at time

Also fridge freezer thought about that and unplugged overnight still tripped
 
Two thoughts...
1 - ramp test it
2 - (obscure one) It doesn't just happen to be very near a smart meter does it?
I'd suspect the smart meter too. Memshield 1 RCBO's will trip when using a UHF 2 way radio whilst working on the DB, so a smart meter communicating could cause it. Next time you're there try sending a text whist close to the consumer unit to see if the RCD trips.
 
I'd suspect the smart meter too. Memshield 1 RCBO's will trip when using a UHF 2 way radio whilst working on the DB, so a smart meter communicating could cause it. Next time you're there try sending a text whist close to the consumer unit to see if the RCD trips.
Hi cheers popping in Tommorow and will try using phone/txt - and just spoke to customer has had this issue intermittent for 4 years - had smart meter since about then one of first ones installed - is only one circuit on MEM RCS/MCB (first Rcbos) and I’m sure has functional earth as well will need to double check
 
Obvious but just swop it out I reckon, see if the problem goes away

Had that said to me a few times about RCDs . Test them and connected wiring and I didn't think to swop them out
 
I'd suspect the smart meter too. Memshield 1 RCBO's will trip when using a UHF 2 way radio whilst working on the DB, so a smart meter communicating could cause it. Next time you're there try sending a text whist close to the consumer unit to see if the RCD trips.
I’ve had this issue myself once, a simple google search pulls up plenty of cases. One chap built a cage around the CU to prove the point!
 
I’ve had this issue myself once, a simple google search pulls up plenty of cases. One chap built a cage around the CU to prove the point!
Hi

Following up I did ramp test 21mA and earth leakage monitored - had 6.4 on the ring circuit Rcbo and overall at meter tails 11mA - I am fitting and new box next week as well doing some other tests to prove the point - I spoke to an SSE engineer who denied everything
 
Hi

Following up I did ramp test 21mA and earth leakage monitored - had 6.4 on the ring circuit Rcbo and overall at meter tails 11mA - I am fitting and new box next week as well doing some other tests to prove the point - I spoke to an SSE engineer who denied everything

I would run a few extension leads to plug in fridge freezer etc from upstairs ring so that absolutely everything was disconnected from the downstairs ring.. This would tell you if its an appliance.

Really interesting comments about smart meters, I wonder if you could shield it some how.... Tinfoil?
 

Reply to MEM RCD/MCB tripping during night in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
881
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
395
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock