Discuss metal capping not needed according to 17th in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
0
Is metal capping required on a new installation in a house to protect the cables if a rcd is used ? According to two lads who i work with have done there 17th ed last week it is not needed so is it only for protexting cables while been plastered ?
 
It is not required. Favoured,specified,preferred,but not required. Careful plasterers negate its use...:icon12:
 
Is metal capping required on a new installation in a house to protect the cables if a rcd is used ? According to two lads who i work with have done there 17th ed last week it is not needed so is it only for protexting cables while been plastered ?

As already said, never required but often used.
It cannot be used as mechanical protection for the cables if not RCD protected and buried less than 50mm
 
if someone was to bang a nail the capping wont help. but it will make extracting the cable for repair much harder.
i`m filling my chases with some bonding coat, no cables on show when plasterer comes do his job, no problems later.
 
capping is pointless really, but is something most electricians like myself like to do.
i thought there was once a reg, for reasonable protection from the plasterers trowel.
 
I always thought it was a rule of thumb or best practice, If the width of the chase is greater than 3/4 of the width of the plasters trowel capping is needed???
 
It would be wise to use plastic capping on bare inners leafs that are going to be floated. It keeps the cables tidy and together (if there is more than one) and gives enough protection against a trowel, its common sense really.
 
Absolutely terrible that anyone would think this in acceptable practice.
 

Reply to metal capping not needed according to 17th in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a two metre length of 2.5mm T&E running from the loft to a spur under galvanised metal capping (installed during building). Its needs...
Replies
25
Views
2K
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
481
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
882
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock