I all 4 bedrooms in a rented property, there are cheap metal electric wall heaters. By design their cables are made of two wires - no cpc.They are plugged into a socket circuit with 32 A MCB.How would you code that? AThe heaters are not part of the installation, do i need to put that in the report?
 
I all 4 bedrooms in a rented property, there are cheap metal electric wall heaters. By design their cables are made of two wires - no cpc.They are plugged into a socket circuit with 32 A MCB.How would you code that? AThe heaters are not part of the installation, do i need to put that in the report?

Are they class I or class II?

Edit: posted same time as DS
 
If they are plugged in, no code as they are not part of the fixed wiring.
you may want to put a note on the report if infact they are class 1 appliances

if they are class 2 then there is no issue.
 
Regardless of whether they're plugged in appliances or not, you've identified a potentially dangerous situation. I would not be happy to walk away from that without first confirming whether the heaters are Class I or Class II.
If they are Class I then I would feel obligated to point this out to the owner, perhaps by way of a comment on the EICR, or in an email.
Although I suspect they're actually Class II.
 

Reply to Metal electric wall heaters - no cpc present. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
204
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock