Discuss Meter tails in the UK Electrical Forum area at ElectriciansForums.net

I think the 3m is an historic answer to our question. There needs to be a limit so DNO fuse will melt when required, and with TNCS and 25mm tails I think technically it could be a lot longer than 3m. For example 88-2 80A fuse needs 400A to melt in 5 sec, and this is a fault loop of no more than 0.575 Ohms at 70C. DNO quote 0.35 Ohms as max for TNCS so 0.575-0.35 = 0.225 Ohms left for tails. So assuming 25+16 is 0.875+1.4x0.8 = 2 mOhms per metre. And so tails 100m long would still provide ADS, unless I've messed it up (always possible). This was just out of interest and it's DNO call anyway. o_O
 
If there were a 100 amp fuse in the cut out and we had to account for discrimination,we would end up putting a 2 sizes lower fuse (63A )to have any chance

The client could become unhappy losing a fair portion of their capacity for no apparent benefit if that was the case

So the point of putting a 100a switch fuse after a 100amp cut out fuse is?
 
So the point of putting a 100a switch fuse after a 100amp cut out fuse is?
I think the point, is that the DNO have no control over what may be installed beyond the meter. Some numpty might come along and run a bit of bell wire to a DB for all they know. In the case of a switch fuse 4M from the cutout then under a low impedance fault then obviously both devices are going to go, even if it is as low as 63A. They are trying to put the responsibility on the installer to make sure the cables beyond their equipment are adequately protected, which their fuse may not?
 

Reply to Meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
We have a meter EDMI - ES30B fitted to our property. I understand from the fact sheet for the smart meter...
Replies
13
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
487
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock