Discuss minor works cert for new circuit doubled up from an existing mcb?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

Guest112

hi guys hoping you can settle a debate i had in work the other day a colleague of mine has been issuing minor works certs for the above explained situation but i asked him why he isnt issuing EICs when he does this he said its because its an existing circuit and hes just adding to it from the db???

seems wrong to me and rough tbh any input on this one?

thanks
 
Well if you take his argument to its logical conclusion as you can turn off the whole board via the 60947 main switch then the whole system is just one circuit, load of old rubbish. your right ,hes wrong
 
Sounds like your colleague is correct, additions to a circuit can be covered with a MWC. If he were to change the protective device or install a RCD or RCBO then a EIC would be required.
 
nope. if the new work is supplied from existing MCB that already supplies a circuit, then the new work becomes part of the original circuit.
 
Well if you take his argument to its logical conclusion as you can turn off the whole board via the 60947 main switch then the whole system is just one circuit, load of old rubbish. your right ,hes wrong
well as it`s still a new circuit..( ok ...yes, its cheeky to take it from an existing circuit at origin but theres nothing to say you cant do this)......but its STILL a new circuit and as such is subject to an EIC.......
 
Of course not but are you seriously saying that by adding another circuit to an MCB that its the same circuit as the one that was there before? Its a new circuit so it needs a EIC

You can't add another circuit to an existing circuits MCB that already as a circuit in it. Reg 314.4.

But if your using the MCB as a JB, and extending the circuit as in post 4 then your fine
 
nope. if the new work is supplied from existing MCB that already supplies a circuit, then the new work becomes part of the original circuit.

110% CORRECT!! Not by any means good practice, but none the less it remains as a single circuit!! It's not possible to have 2 or more circuits supplied by a single protective device!!!
 
110% CORRECT!! Not by any means good practice, but none the less it remains as a single circuit!! It's not possible to have 2 or more circuits supplied by a single protective device!!!
allright...i get your drift eng mate.....time/current ....back to a single point at source and all that but.....lets say that the original/existing circuit served 5 points......typical for a small house down lighting circuit.....and the new feed consisted of.....lest say 8 or 9 points......
 
Does anyone here actually like filling out fekin certs? If I can get away with an MWC instead of an EIC-more power to me, the customer still gets the same job done at the end of the day. Having said this I would never use it as an excuse to NOT add an mcb, now that is rough.
 
Does anyone here actually like filling out fekin certs? If I can get away with an MWC instead of an EIC-more power to me, the customer still gets the same job done at the end of the day. Having said this I would never use it as an excuse to NOT add an mcb, now that is rough.
well of course if you were to drop an MCB into the C/U for a NEW CIRCUIT......and run a circuit from that....as this would be clear...then it would be an EIC.....
 
or what you could do is to take the line from one side of the C/U.....and the neutral from the other side.....a sort of shared responsibility if you like....half the circuit..half the cert...seemples....
 
Glenn as long as you comply with Regulation 433.1.1 regarding cable protection and disconnection times for the protective device you shouldn't have to many problems of how many actual lights are on the circuit.

Also of course you will have the 3% volt drop to consider.
 
Well I`ll bow to superior knowledge. Seems amazing to me that, in theory, you can put a single socket outlet supplied via a new 2.5mm cable into a 32amp MCB supplying a ring, call it a junction box and issue a MWC but hey ho.
 
Last edited:
Glenn as long as you comply with Regulation 433.1.1 regarding cable protection and disconnection times for the protective device you shouldn't have to many problems of how many actual lights are on the circuit.

Also of course you will have the 3% volt drop to consider.
yes Malcolm.....what you will have covered is all the norms.....and i would also assume that if not surface run and at a depth of less than 50mm...n all that lot.blah blah blah.....then the existing MCB is replaced with an RCBO....and earthing + bonding (both main and supplementary)...were checked first....and upgraded ..if necessary....
 
thanks guys yes bonding was all checked prior to beginning the circuit was run in trunking throughout and was supplying additional fittings, access to existing fittings was the issue so the soulution for him was to run the feed from the db rather from another local fitting, bit of a funny situation i was leaning towards the eic side tbh but you live and learn, there was only one existing feed from the mcb and it supplies the lighting that couldnt be tapped off in the first place so not as bad as it could be, personally i dont like more than one conductor in a protective device unless its a ring but thats me thanks for the input
 
Well I`ll bow to superior knowledge. Seems amazing to me that, in theory, you can put a single socket outlet supplied via a new 2.5mm cable into a 32amp MCB supplying a ring, call it a junction box and issue a MWC but hey ho.
that would be adding a single socket outlet as a spur. just as if you spurred from a socket outlet remote from the CU.
 

Reply to minor works cert for new circuit doubled up from an existing mcb?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Morning all. I was chatting with another spark the other day and he’s telling me I’m making excessive work for myself by issuing minor works...
Replies
11
Views
3K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
898
HI EVERYONE, IF I ADD A RADIAL CIRCUIT OF 2 SOCKETS , 5 METER RUN IN 4MM FLEX CONTAINED IN CONUIT AND TRUNKING, AND TERMINATE IT IN AN EXISTING...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock