startout2007

i have just looked at a strange house with loads of extensions done. the board isn't labbled up. on turing off the mcbs on two ring circuits its still live unless both are turned off. so i assume at some time a link has been bodged in between the two rings for some sockets. whats the best way to try to find the problem as the house is a right jumble.thanks
 
i would assume that the house was wired in 2 rings, but when connected into the mcbs they put 1 leg of 1 ring with the other and vice versa. i have come across this before
 
first thing is to do a continuity check on all of the cores of the two rings (you never know the rings could be inter-connected at the board due to a CU change or something).

if you have 3 or 4 line conductors from the 2 rings with cont. between then you've got a problem

it would be unsusual for a diy expert to connect to live sockets to each other, they just have a habit of sharing a supply to the place where they want it at the time

i would assume that the house was wired in 2 rings, but when connected into the mcbs they put 1 leg of 1 ring with the other and vice versa. i have come across this before


ooh beat me to it :D
 
Last edited by a moderator:
first thing i would do is go around all of the sockets and note which ones have more than 2 t+e connected. see what you're up against
 
not sure really, it was late when i posted that (and i'd had a little drink)

but if he'd proved there is an interlink in the circuit somewhere, if you find 3 or more cables in a back box, it would be an immediate suspect for the interlink.
 
Unless theres a section that looks suspect

Maybe concentrate on one leg at a time
Link out live and earth of that one leg and go round taking the readings as per a radial etc

It may give you an early indication of what rings were intended or original,perhaps having a beter start point for the slog
 
thanks for your ideas that was the way i was thinking looks like the isnt a easy answer i will let you know when i tackle this in a weeks time.
 
starting a job on monday the same sort of problem. got three line conductors into one old syle fuse feeding both upstairs and downstairs ring. also lighting circuit for whole house on one circuit. think me going to have fun. so going to get missus to shave me head tonight, stop me tearing it out tomorrow, lol:confused:
 

Reply to mixed ring circuits linked in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
837
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
277

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock