Scott_fd2r - A quick contribution - you don't specifically mention it so:
1. Are you providing a single phase supply to this single phase motor? ie: Is the supply derived from a split phase transformer L1-N-L2 (viz 240-0-240V) or are you using L1, L2 and N from a three phase 4 wire 415V supply?
2. What is the supply voltage at the Brook starter L1-L2, L1-N and L2-N before starting, during starting and when running?
1. Are you providing a single phase supply to this single phase motor? ie: Is the supply derived from a split phase transformer L1-N-L2 (viz 240-0-240V) or are you using L1, L2 and N from a three phase 4 wire 415V supply?
2. What is the supply voltage at the Brook starter L1-L2, L1-N and L2-N before starting, during starting and when running?