today I was back at the motor,
the voltage is only around 220v at the starter. during starting this can drop to around 212v, during running its is around 218v.

everything has been ok since i was last there, but i am told the mill/bruiser throughput is less than with the previous motor. i did some load tests. the motor draws around 36A at startup and quickly settles to around 11A. as the grain flow is increased the load rises to around 15A. at this flow the operator says it will run constantly with no problem. if the flow is increased further the load can rise to around 20A but at this rate the current is very unsettled jumping from 18-22A the voltage remains steady at 218v. if the flow is increased by just a fraction more the load jumps to 30+ amps and the motor stalls and sits humming until it is stopped or trips.
the rpm never alters much from 1400 just drops immediately as the current shoots up and the motor stalls

i checked the current on both windings at each stage and the windings appear well balanced with the currents exactly the same at each stage. (half of the total load drawn).

they are happy to leave it like this for now and run with a reduced flow rate until the other motor is rewound and refitted. just posted this info incase anyone was interested
 
Hi all, thanks again for any input.
I have been asked to look at this starter as motor starts ok, but when switches over to run motor stops and starter just hums.
First of all like I’ve said in previous posts I haven’t had a lot of experience with motors/ starters etc
Am I right in thinking this starter is for a capacitor start - capacitor run motor with no centrifugal switch as it has a timer set to 15 seconds and then 3 contactors?
The motor starts ok and contractor in middle kicks in and contractor on right kicks in but after time delay right contractor drops out, but left one doesn’t kick in.
The part I’m not sure about is that there is a 1M ohm resistor across the 13 and 14 contacts on the left contractor and if I bypass this with some cable it all appears to work fine. I have checked resistor and it reads 1M ohm like it should ( brown, black, green and gold).
Could anybody tell me why the resistor is there in the first place and what it does ( is it to stop a back feed?) and why the starter seems to work fine when I bypass it yet it is reading ok???
Thank you
[automerge]1575303628[/automerge]
Also forgot to mention there is a cable from 14 terminal to A2 of run contractor..
Is this a SP OR TP Motor?
 
Its single-phase, but it turned out to be a 480V motor that had been installed second-hand as a replacememt by mistake on a 230V supply and also incorrectly wired internally at the time the OP first encountered it. The behaviour is consistent with the voltage mismatch, as at 1400 rpm it's running below rated full load speed even at moderate load. Unfortunately an earler measurement of the speed in post #41 indicated it was reaching 1490 rpm off load which suggested the voltage was correct.

Thanks for the update @Scott_fd2r, it's good to hear the original motor is being rewound.

E2A Pete that first post was actually about a different motor from last year
 
Re:
today I was back at the motor. the voltage is only around 220v at the starter. during starting this can drop to around 212v, during running its is around 218v.

The off-load supply voltage at the starter is somewhat low at 220V. Is this the voltage at the input terminals of the main switch for the building? Does the building have a high current demand from permanently energised loads which is causing a significant voltage drop? What voltage does the incoming supply rise to when the building's main switch is opened?

As a simple rule of thumb the power of a motor is proportional to Vsquared so a motor wound for 240V would produce about (220/240)squared = 80% of its rated power output. Is the motor powering the machine often required to operate at rated power? Could this be a factor in why the previous motor burnt out? Some thought then into what voltage to rewind the motor to operate at.

And an investigation as to whether the incoming supply is 'weak' because of some external high resistance connection. What for example are the line-neutral voltages in neighbouring buildings using the same DNO distribution cables - could you measure these?
 
Evening, I have a similar issue with a grain mill where farmer has given me a 5hp motor and this starter box. Connections to A1,A2,A3 and A4 seemed straight forward but the 2 capacitors in series that go through the first stage contactor on left (red and white wire in con block) I am unsure of terminals to attach to on motor. Any help please? They come out of connection on second stage after a 4 second timer.
Stage 1 main contactor (with O/L) and left contactor go in, controlled by timer on left. Stage 2 middle contactor and main contactor go in.
thanks in advance
 

Attachments

  • IMG_2333.jpeg
    598.2 KB · Views: 7
  • IMG_2331.jpeg
    621.3 KB · Views: 7
  • IMG_2329.jpeg
    570.8 KB · Views: 9
  • IMG_2328.jpeg
    522.6 KB · Views: 9
Evening, I have a similar issue with a grain mill where farmer has given me a 5hp motor and this starter box. Connections to A1,A2,A3 and A4 seemed straight forward but the 2 capacitors in series that go through the first stage contactor on left (red and white wire in con block) I am unsure of terminals to attach to on motor. Any help please? They come out of connection on second stage after a 4 second timer.
Stage 1 main contactor (with O/L) and left contactor go in, controlled by timer on left. Stage 2 middle contactor and main contactor go in.
thanks in advance
Do you still want help with this or have you fathomed it out already?
 
New posts

Reply to Motor starter help. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening all Ive got an old truck 1990 that has always had intermittent starting issues whilst ive owned it.. As far as i am aware the...
Replies
11
Views
921
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
660
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
Hi all Back in July last year I installed a new pool pump/motor. The problem is it's now making a humming noise and trips the breaker. I...
Replies
21
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock