before changing db you have to prove that the installation is ok to accept 17th edition boards a landlord has asked me to change 12 in a block of flats now usually i would do full test on boards but bearing in mind the prices are tight not wanting to spend to much time would i get away with just an insulation test between LN together to earth your thoughts please
 
visual inspection, then IR . test for borrowed neutrals. if you have an earth leakage clamp meter, check if there's any apparent earth leakage. measure Ze. CONFIRM EARTHING AND BONDING. lack of bonding can bite you in the pocket.
 
Last edited:
The above tests should be enough to change the board and if the IR tests are 8 Meg and above the RCD's will hold no problem at all.

Its the unexpected faults that you have to look for ie no continuity on final rings ccts very high R1 +R2 readings on radials which need further investigation etc etc.
 
if time allows, might be a good idea to take a few Zs readings and end/end continuity of RFC/S.
 

Reply to multi consumer board changes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
What certification do I need when replacing a consumer unit ? Here are the details. I am semi retired (electrician) and work for a company as...
Replies
48
Views
8K
This is getting embarrassing - I've been looking for a sub-main consumer unit in a church for an hour now. I've found the incomer. There's a nice...
Replies
52
Views
6K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock