Search the forum,

Discuss multi strand 2.5mm T&E - is it OK to use? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Geoff_Potts

Hi, I've been working in a relatively new house (approx 5 years old) and the kitchen ring is wired with 2.5mm, twin and earth in which both the line and protective conductors are multistranded.

Is this OK to use? I've never come across it on 2.5mm cable and they have nuisance tripping on this circuit, just wondered if it was in common useage as I've never seen it before.

Thanks
 
Last edited by a moderator:
No, the IR is poor 0.78, but I've switched off and am returning tomorrow to find the fault. Was just wondering as one of the trade magazines I get has been going on about substandard cable.

I haven't been into disconnecting sections yet, so the IR reading may be a damaged cable, socket or wiring in back box etc. It is not definitely the cable run itself yet.
 
Last edited by a moderator:
Nothing wrong with the flexible multi-stranded single cables Are these singles your talking about, pulled into conduit?? Much more expensive than your solid core variety, and far easier to pull into conduit, especially if you have some tighter bends... Might even have a better current carrying rating too, but don't hold me to that!! lol!!

EDIT... Sorry, you mentioned T&E in your post, ....Only ever seen this type of cable in the Far East, but never used on our progects...
 
Last edited by a moderator:
No they're not singles, it's T&E, but all cores are stranded like 10mm etc.
Thats OK, I've never seen it on 2.5 before so possibly it is used to be more flexible, for some reason it's only the kitchen ring wired with it, rest of house is all solid so I assume the installer had his reasons. Anyway, just wanted to make sure nobody came up with 'it's cheap rubbish, take it out, it's a fire risk!'

So all I have to do now is locate fault and cable shoudl be OK.
 
thats why i asked, theres actually some in my house but under old colours, and that I've seen a bit. I've never seen before this one in harmonised though. Just wanted to make sure there was no reason for/against using it.
 
Just tried NICEIC technical and they're not happy, they've no reg for/against using it but it's not one they've come across in a new build either. Not sure what to do here, don't want to rewire a kitchen if it doesn't need it, but after all the hype lately of banned cables I dont' want to say its safe and have house burned down. I need to find out whats causing the low IR. I suppose if it's machanical fault and it goes back up above 2M when fixed i suppose I'm then safe to say cable is OK to use.
 
This was the norm pre 15th Edition. However, as this is new cable in harmonised colours, I would suggest this Far East imported stock and unlikely to be BASEC approved. Contact BASEC by telephone or Email they will provide technical information / advice and investigate if counterfit/non compliant cable has been purchased, further details at BASEC - British Approvals Service for Cables
click 'About BASEC, Complaints' for more information.
 
Have you access to the runs of cable above a ceiling or similar. You may be able to see if the cable is BASEC approved or similar by looking at the markings on the outer sleeving. Have to admit i've never seen stranded harmonised twin and earth, the only stranded stuff i've seen was old colours and more often then not tinned copper.
 
Hi, I've been working in a relatively new house (approx 5 years old) and the kitchen ring is wired with 2.5mm, twin and earth in which both the line and protective conductors are multistranded.

Is this OK to use? I've never come across it on 2.5mm cable and they have nuisance tripping on this circuit, just wondered if it was in common useage as I've never seen it before.

Thanks
He says in which both the line and protective conductors are multistranded.



Sent from my iPhone using Tapatalk.
 
i read it as both line conductors multi stranded. 2nd read says i misread it.
 
Hi, I've been working in a relatively new house (approx 5 years old) and the kitchen ring is wired with 2.5mm, twin and earth in which both the line and protective conductors are multistranded.

Is this OK to use? I've never come across it on 2.5mm cable and they have nuisance tripping on this circuit, just wondered if it was in common useage as I've never seen it before.

Thanks

if you read th OP , he says the phase conductors are stranded, not the cpc.

If you read the OP properly i think he does mention the CPC is stranded. ;)
 
see my las t post. re-read it . have to go to specsavers. apologies , mate.
 
we all make mistakes, as the hedgehog said, climbing off the bog brush
 
I've never seen this type of cable either. Isn't it as simple as look for the 'kite mark' or similar (underwriters laboratory etc) approval/conformance stamped on the cable.
 
see my las t post. re-read it . have to go to specsavers. apologies , mate.

You must have posted while I was doing so fella! You had me doubting myself as it's been a long old day, sounds like I'm not the only one either! Lol Hope the winking smile provided the right level of wit to my post without sounding like I was being an internet ****, haven't been here long enough to start trolling and upsetting the regulars! :D
 
Last edited:
I've just be checking with Draka and FS cables it seems 2.5 mmsq T&E with stranded conductor is available in harmonized colours, Table 9 of BS 6004 specifies alternative conductor (class 2) options for 1.5 mmsq and 2.5 mmsq stranded conductor twin and earth cable. It's not as common as the solid conductor versions but according to the manufacturers it is available off the shelf.
 
Last edited by a moderator:
Hi

Just seen your post. Although it is an old one I wouldlike to comment on your question in case someone else is looking.
I have only been in this Country since 1990, having originated from NewZealand. In New Zealand everyone uses stranded twin and earth and the earth isalso sleeved. Solid is not used because it is not flexible enough, takes longerto get straight and is not so easily twisted together.
It would seem that the solid here in the UK is used because people do notnecessarily know stranded is available, which it is, in 1.5 and 2.5 twin andearth. I never use solid as I feel it is inferior and a real sod to use.
If people started asking for stranded twin and earth instead of solid then the supplierswould have to make it easier to get. RS have started selling it, by the way.

I find it hard to understand why every other cable youbuy has a sleeved earth yet twin and earth does not. The cost difference issurely minimal.
If you get the chance to buy stranded then do so. Youwill never go back to solid.
 
We used to have stranded, pag. Personally, I hate solid core and love working with the old imperial stuff. I bet the accountants who decided to switch us over to solid-core never had to work with it...
 
I have purchased stranded 1.5mm and 2.5mm twin and earthfrom the wholesalers, but I had to wait for it, as it was not off the shelf.Looking through the RS catalogue recently it looks as though they do it,although I have not yet confirmed this.
 
It would be an extremely good move to have the 1mm / 1.5mm / 2.5mm stranded. The present solid core sizes was one of the worst moves made during the metrification of UK cables!! I'm sure every single electrician here, that has worked with the older stranded imperial cables, would wholeheartedly agree!! lol!!
 
never seen 2.5 multi stranded twe in harmonised colours only in OLD cables

About time the UK caught up. Been using stranded power cables in Australia for years. As for cost?? It was actually cheaper there to buy stranded than solid, as no-one used solid, preferring the cable that is far far easier to work with and terminate.

Alas, I rarely do electrical work here in the Uk. Guess I have been spoiled, hey?? :)
 
About time the UK caught up. Been using stranded power cables in Australia for years. As for cost?? It was actually cheaper there to buy stranded than solid, as no-one used solid, preferring the cable that is far far easier to work with and terminate.

Alas, I rarely do electrical work here in the Uk. Guess I have been spoiled, hey?? :)

I don't know why the UK doesn't make more use of stranded cables, they are far superior than that of the solid core cables

Think i've already mentioned on a previous thread that we only use stranded metric cables on our project, we just don't use solid core cables. Come to that, you won't see any T&E cable on this project either!! lol!!
 
I don't know why the UK doesn't make more use of stranded cables, they are far superior than that of the solid core cables

Think i've already mentioned on a previous thread that we only use stranded metric cables on our project, we just don't use solid core cables. Come to that, you won't see any T&E cable on this project either!! lol!!

Do you use stranded wiring like cabtyre (HO7RNF type) cable images2.jpeg

or much courser stranded like house wire? images.jpeg
 
About time the UK caught up. Been using stranded power cables in Australia for years. As for cost?? It was actually cheaper there to buy stranded than solid, as no-one used solid, preferring the cable that is far far easier to work with and terminate.

Alas, I rarely do electrical work here in the Uk. Guess I have been spoiled, hey?? :)

About time the Australian internet caught up with the UK, this thread had been dormant for over a year.
 
Easier to install, not so sure about being easier to connect, I prefer it but that's my choice
 
Haha yes of course i 've worked with it but terminating stranded always is a hassle and a struggle when trying to put a few in one terminal. Not to mention that you cant use my beloved push in wago connectors with the stuff !!! ;-)
 
As a 'newbie' just out of interest why do you old schoolers prefer stranded? I prefer solid hands down!


Because there is no comparison between stranded and solid core, None!! A stranded conductor is the absolute winner over a solid core conductor every single time, far more flexible and because they have a larger surface area, a higher CCC!!

Why is terminating a 3 or 7 strand cable difficult FFS, ...it's also going to be a far more secure termination into wall accessory plates and protective devices than solid core.
 

Reply to multi strand 2.5mm T&E - is it OK to use? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket. The three solid cores rarely sit cleanly, and there's always the...
Replies
45
Views
5K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
700
Recently a couple of threads have discussed T&E cable and it became apparent to me that the 2.5mm, which I have only ever seen as solid core, is...
Replies
47
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top