Discuss My first EICR and I'm confused! I'm industrial this is domestic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

All the sockets are fine.
When separating the legs I've identified which sockets are on which side.

Fortunately as only one ring socket is on one leg I'm pretty certain the fault lies between that socket and another. Finding the 'another' will be a faf.

My next step is to remove all the ring socket covers and separate the cables. A bit of long leading the N will help find the dodgy leg.

I can then remove that one cable from each end leaving (hopefully) two spurs.

What a faf.

I hope the actual exam isn't this bad or I'm going to run out of time massively!
 
If the fault is near to one end of the RFC, you are going to end up with a spur that loops back on itself, so are going to end up with a spur that uses much more cable than one that was designed as a spur from the start.
You will need to check that loop impedance and voltage drop are all acceptable, and access the likely maximum load of the circuit, to ensure it doesn't exceed the rating of the smaller MCB.
 
All the sockets are fine.
When separating the legs I've identified which sockets are on which side.

Fortunately as only one ring socket is on one leg I'm pretty certain the fault lies between that socket and another. Finding the 'another' will be a faf.

My next step is to remove all the ring socket covers and separate the cables. A bit of long leading the N will help find the dodgy leg.

I can then remove that one cable from each end leaving (hopefully) two spurs.

What a faf.

I hope the actual exam isn't this bad or I'm going to run out of time massively!
Rather confused by the fact that you have identified what sockets are on each side of the fault but then you say you haven't and that finding the other socket on the ring will be a faf

I would suggest buying a cheap continuity tester https://cpc.farnell.com/tenma/ten01049/continuity-tester/dp/IN05723 rather than spending a lot of time removing all the sockets

With the continuity tester you can work along one leg of the ring quite quickly and identify where the break is and then do the same on the other leg which should bring you to a point where you can then diagnose the cause of the fault and repair the ring
 
The zs/rn readings are so low that they are useless for analysis.
What are you using to measure things?

Generally speaking Zs measurements are not that precise, not when you get down to under an ohm and more so if "no trip" due to RCD action so testing at very small L-E currents, so you are unlikely to get far finding a RFC break on that alone.

However, DC low ohm measurements using a typical MFT or similar usually are good enough but you have to allow for dirty switch contacts and socket pins so sometimes you have to insert/remove the test plug adaptor (or lead) a couple of times and operated the switch a could of times to get a low stable reading.

Even then you are likely to only reliably see differences in cable distance of several meters as, for example 2.5m T&E has R1+R2 of about 0.02 ohm/meter and (I guess) most low ohm meters likely to be at hand resolve around 0.01 ohm.
 
I don't think that is CAT rated, so I would rather not use it on anything that might be live!

Maybe a cheap voltage tester that has a continuity buzzer?
So is he is going to disconnect all the sockets while they are live, I think that would be a no

Given the OP is an industrial electrician I would like to think he would be able to use a simple continuity tester to locate a simple ring circuit fault
 
I'm using a Megger mft1721.
I've also got my fancy multimeter for precise testing.

You're right, the Zs is useless for this, I'll do a dc test as that may have more accuracy. Good tip, thanks.

What I'm hoping is that the failure is directly between two ring sockets. All I need to do is identify the cable between and disconnect it at both ends.
If that is the case then I know which socket is on one side. I don't know where the next one in the supposed ring is (there are 3 probables).
Unfortunately I don't know where the spurs cut in, which adds a wild card.



Hopefully the accuracy of the r1rn dc test will give clues.

As for splitting the ring, my whole house was using 14A in total. This circuit is just skirting board sockets. Unless I suddenly start loving electric room heaters the load will be limited.

Now the question is do I fit the b16 from my spares, or go buy a b20 ;)


P.s. That's a good tip about turning the sockets off before splitting them too. I wish I'd known that last night as the burns on my hands are really smarting this morning 😂
 
I'm using a Megger mft1721.
I've also got my fancy multimeter for precise testing.

You're right, the Zs is useless for this, I'll do a dc test as that may have more accuracy. Good tip, thanks.

What I'm hoping is that the failure is directly between two ring sockets. All I need to do is identify the cable between and disconnect it at both ends.
If that is the case then I know which socket is on one side. I don't know where the next one in the supposed ring is (there are 3 probables).
Unfortunately I don't know where the spurs cut in, which adds a wild card.



Hopefully the accuracy of the r1rn dc test will give clues.

As for splitting the ring, my whole house was using 14A in total. This circuit is just skirting board sockets. Unless I suddenly start loving electric room heaters the load will be limited.

Now the question is do I fit the b16 from my spares, or go buy a b20 ;)


P.s. That's a good tip about turning the sockets off before splitting them too. I wish I'd known that last night as the burns on my hands are really smarting this morning 😂
While splitting the ring is an easy fix and while it is very rare that a cable is at fault I think actually locating / repairing the fault would be more beneficial from a learning point of view for you
 
So is he is going to disconnect all the sockets while they are live, I think that would be a no

Given the OP is an industrial electrician I would like to think he would be able to use a simple continuity tester to locate a simple ring circuit fault
Here, no it should be fine to use that kit.

It is more of a general dislike on my behalf of having test equipment that is not mains-fault rated in use where mains is about. Sooner or later we all make a mistake and probe the wrong circuit (or discover they are mislabelled somewhere) that is live, and then having something that does not explode on you is nice.
 
Here, no it should be fine to use that kit.

It is more of a general dislike on my behalf of having test equipment that is not mains-fault rated in use where mains is about. Sooner or later we all make a mistake and probe the wrong circuit (or discover they are mislabelled somewhere) that is live, and then having something that does not explode on you is nice.
I think we all knew what you meant.

Exploding kit aka audiovisual alert.
 

Reply to My first EICR and I'm confused! I'm industrial this is domestic in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
900
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I rather foolishly booked in a fault finding job in a 2 hour slot thinking I could solve it quickly, I couldn't! It has me confused, although I...
Replies
23
Views
2K
Hiya. For anyone interested in domestic fault finding I had a funny one today... Customer complained about her bs 3871 popout kept popping on...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock