Update went to site couple of days ago and probably back there tomorrow to look further into it all,
So as I think I said 1 x B50 Hager rcbo at 30mA supplying house c/u and then all circuits there are on standard Hager mcb's carried out rcd ramp test and auto test and always tripped rcbo supplying c/u at 21mA rising or falling waveforms and then tried IR also as only 4 x sockets in room which is the issue ! one in hallway apparently done away with as it "melted" I was told !

IR was starting at around 2.6Meg at 500V and rose to around 3.6 Megohms / Megaohms as it dried the cables out. Not good at all, one socket backbox was different.... in the way that a piece of wood much bigger had been screwed onto the wall to effectively blank off the metal box and on wood had been fitted a 2 gang pattress and double socket outlet, I thought that was strange so I unscrewed it to be nosey, and found that the said dampness in room had turned the original backbox into flakes of rusty steel and no longer had any real resemblance to a metal back box at all and cables x2 twin and earths were covered in either oxidisation / verdigris or green goo or both ! Now barring the computers and other weird and wacky electronic kit in there I'm not surprised the rcbo trips on occasion ! taking the entire house c/u out in the process. Now I have got myself a B50 Hager mcb to replace the rcbo feeding the house c/u and a couple of rcbo's to put on the sockets down where issue is from main house c/u to test if that holds better ? whether dampness or the computers etc.. also Zs readings were fine and weird one which I haven't seen before is what looks like normal ring connected 2x 2.5mm's in sockets but at c/u a single 4mm twin and earth at 20A mcb ?? like it leaves now on a 20A radial arrangement and is somewhere jointed onto a ring as it links sockets ? Surely not on ? even though is only on a 20A as a radial so covers the 2.5's ! Only other option is to rewire the room with new cable and hope the damp gets sorted sometime, but only way she'll entertain that is via mini trunking surface on hall ceiling from c/u and then along high on walls of room and dropping to each socket all surface mounted.
 

Reply to Mystery Black Box ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock