customer currently has a 1 double socket spurred directly from the ring main 32AMCB (piggy backed)in 2.5mm cable directcly under the main consumer unit. He is wanting to add another socket. Note no spare ways in Consumer unit and no other sockets within room. RCD protection present

if the existing spur socket is turned into a fused spur (13amp fuse) then it would be possible to now add an additional socket

as the 2.5mm cable can now only draw a maximim 0f 13amps and is back fused by the cartridge fuse in the fused connection unit as with any fused spur addition

im sure my thinking is correct but you never know

many thanks.
 
fit a 13A FCU, then you can add as many sockets as you want to the spur, although too many would perhaps lead to the 13A fuse blowing.
 
You could insert an FCU before the existing socket and then have more sockets after (or before) the first socket so long as they are all fed from the spur..
You can do your replacement of the socket with an FCU and add more sockets afterward.
You could run another piece of 2.5 from the same breaker to another double socket, so you would have two spurs from the CU, there is a limit to this as you would not want to draw too much before the ring, but at the origin is the best place.
 
you couls also divert 1 leg out of the CU into a socket, then back through more sockets into the cU, thus extending the RFC and negating the need for FCU.
 

Reply to Need clarification of my thinking in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
789
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
981
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
798
I’ve had a disagreement with one of the Engineers in work. So we are doing an install. Installing an Intruder Alarm. Rather than go with my...
Replies
48
Views
6K
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock