Light won’t turn on, swapped everything up to that terminal block with the same light type in another room and they all work, the block is the next part I haven’t swapped over, I have swapped switch over aswell that works as normal so it’s either the block or a wire failure
 
Can't really see that it is the fitting/connector that has failed...looks robust and simple enough, and an easy workaround if not.

Something wrong in the wiring, methinks.
 
Light won’t turn on, swapped everything up to that terminal block with the same light type in another room and they all work, the block is the next part I haven’t swapped over, I have swapped switch over aswell that works as normal so it’s either the block or a wire failure
You have got to do some testing here.
Find out if you get 230v to the point of connection if so you have to test continuity on all cables in that fitting.
 
I tend to agree with dmxtothemax, there doesn't appear to be any sign of burning on the connection so either you don't have 230V at the supply or the electronic ballast has failed, assuming it has one. Put a test lamp across live and neutral and check you have both present. Plug the thing in and check you have both live and neutral on the plug side.
 
BTW if you are live on the socket side but not on the plug side just joint the cable together, perhaps with click wagos, assuming there is no protective/control device in the plug. If there is a protective/control device in the plug either replace it or buy a new light.
 

Reply to Need electrical advice failed part and need replacement but unsure of part name pic included in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
485
  • Article
Electrical2Go - Save Time Installing Cables with Super Rod At Electrical2Go, we're constantly striving to bring you the latest and most...
Replies
0
Views
100
Hello all, I’m looking for some advice regarding a recently broken MVHR unit in my flat, model Heatrae Sadia Advance. The unit is out of...
Replies
0
Views
738
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
788
  • Article
Electrical2Go - Save Time Installing Cables with Super Rod At Electrical2Go, we're constantly striving to bring you the latest and most...
Replies
0
Views
507

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock