Hi all , We are carrying out a refit on a retail unit and the client wants us to provide a clean dB for the till power and the data cab. Can anyone clarify best practise for configuring this in the install .
The site currently has a 3 phase incomer with 60a fuses at the distributors side.
We are intending to install a schneider acti 9 TPN 8 way board with a 125A 4pole switch isolator to feed the general lighting and power. .
The intention was to go Into Henley blocks from the meter and then split to the TPN and off to a single phase board for the clean power . Is this correct ?

Many concerns are
1. If I install like this will the phases not be unbalanced ?
2 am I better off supplying the clean dB from a MCB in the TPN board?
3 can anyone give me general advice on best practice for balancing 3 phase DBS.

i know this is a large topic .

Any advice and help would be grateful . Many thanks in Advance
 
well a dedicated supply and mcbs to provide power to kit like the pdq machine and the data cab . So in the event that the general power is interrupted it doesn't cause issues with the tills .i.e a mcb powering the ring . It's fairly common is supermarkets
 
I would recommend coming of your main distribution board to supply your Dedicated supply DB as Dilld says you could spred the load by the way you configure the main DB or you could fit a small 3 phase 4 way DB it depends how many circuits you need if its just a till socket and a coms cab just run 2 separate circuits from your main DB and not bother with the separate board ,Unless they want a last man out switch then that changes everything
 
They do want a last man out but I'm installing contractors for just the lighting for the last man out. Ok so the two options are feed db2(single phase clean dB) from mcb in TPN (db1) or to fit Henley blocks then From there feed db1 and db2 . Is that correct?
 
I've re read post 11 .dont mean to sound dumb but surely if iinstall with Helena blocks and feed both dbs . Each dB has a switch isolator therefore isolating the supply ? Or am I missing something here?
 
Hi all , We are carrying out a refit on a retail unit and the client wants us to provide a clean dB for the till power and the data cab. Can anyone clarify best practise for configuring this in the install .
The site currently has a 3 phase incomer with 60a fuses at the distributors side.
We are intending to install a schneider acti 9 TPN 8 way board with a 125A 4pole switch isolator to feed the general lighting and power. .
The intention was to go Into Henley blocks from the meter and then split to the TPN and off to a single phase board for the clean power . Is this correct ?

Many concerns are
1. If I install like this will the phases not be unbalanced ?
2 am I better off supplying the clean dB from a MCB in the TPN board?
3 can anyone give me general advice on best practice for balancing 3 phase DBS.

i know this is a large topic . 

Any advice and help would be grateful . Many thanks in Advance

So what does the contract tender specifications call for, a so-called clean/dedicated DB or clean/dedicated MCB's, there is a mountain of difference in project cost here??
 

Reply to Need help with clean dB on retail unit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top