Discuss Neutral wiring problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Thanks, think I might just have a bath ha ha. In all seriousness it should be sorted on Friday. Why isn't the earth already sleeved like the other two wires?

There's no real need for the earth conductor to be sleeved in the fixed twin and earth wiring, as the 2 live conductors are insulated. Obviously it just needs a small piece of sleeving adding wherever it enters an accessory though.

Spin got there before me with another good reason!
 
The switch front is plastic.
Terminating the earths in the front plate, will only earth the screws.
The screws getearthed by being in contact with the metal back box which is already earthed.
Shame we can’t do dumb as well as disagree.
 
Ok, thanks. So the wires that are connected to the back box at the moment should be re connected to the switch plate directly. Then a earth wire from the plate to the back box terminal? Forgive my ignorance but what's the difference between the two?
 
Ok, thanks. So the wires that are connected to the back box at the moment should be re connected to the switch plate directly. Then a earth wire from the plate to the back box terminal? Forgive my ignorance but what's the difference between the two?
The switch you have is rated for up to 45A.
That usually means it has much larger wires connected to it.
Wires that would not fit into the earth terminal in the back box.
So the manufacturer’s provide the larger earth terminals so you can terminate the larger earth wires.
As you are not using large wire, you don’t need to use the large earth terminals.
 

Reply to Neutral wiring problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
699
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
533
Hello, I’m trying to change a pendent light, I’ve wired it the same as the previous light that was on there however the light is now permanently...
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock