Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
 
Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
All electrical points require a cpc (earth wire) whether used or not
 
Either I'm going blind or it's not in the book that every circuit shall have a CPC?

Sanity check please, 543 onwards.
 
Have a closer look, guess the new build sparky has snipped off the annoying earth wire; it'll be hidden inside the outer sheathing.
 
you might want to check all the lighting points for a cpc. Switches and lights.
I would think a new build domestic property would be wired in grey twin and earth.... and the earth is there, just cut off.
It could be a pain if there’s not enough spare cable to pull
 
Every point in the wiring (not just every circuit) must have a cpc terminated. So obviously a cpc is required at a luminaire, whether inside or outside.
But where is it written? I'm not being pedantic, I can't find it in the book.
 
06F8DAA9-E33A-4BBA-8A17-11E5F1AAB986.jpeg
 
While we’re on he subject then, if say a klix box has a cpc to it, I am ok to plug 2c off that to class 2 fittings?
I would personally say that the cable from the klix box should be at least a 3 core (containing a cpc) as it is not the same as a lamp holder given as an exception in the regulation unless your primary means of protection is the protective measure double Or reinforced insulation which is not permitted in a domestic installation.
 
New posts

Reply to New build outside light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Replies
3
Views
547
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
455
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
533
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi guys, medium to beginners experience in electrics. I placed a 250w security PIR light outside. I connected it to the inside first-floor...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock