Discuss New circuits. in the UK Electrical Forum area at ElectriciansForums.net

J

joehat

Hi all

I'm. Installing new circuits into a metal db with 10mm twin and earth as the tails into the main switch, so I can only assume their is a submain but my issue is the garage it's choca and we think it's where the main fuse is, would anyone be happy to put lim in this situation with the fuse ect/submain , as I am only from the house db adding circuits?

As in I can't put any details in as the main switch or submain board..can this be lims as I can't get to any of this?

Sent from my SM-G930F using Tapatalk
 
Last edited by a moderator:
Hi all

I'm. Installing new circuits into a metal db with 10mm twin and earth as the tails into the main switch, so I can only assume their is a submain but my issue is the garage it's choca and we think it's where the main fuse is, would anyone be happy to put lim in this situation with the fuse ect/submain , as I am only from the house db adding circuits?

Sent from my SM-G930F using Tapatalk


Joe, confused.com
 
i think what he's saying is that the intake and main DB are in the garage and it's full of crap so he can't access it to get details.
 
Sorry if I didn't explain very well but yes Tel

There's main bonding in the db in the house to gas and water,

Sent from my SM-G930F using Tapatalk
 
Hi all

I'm. Installing new circuits into a metal db with 10mm twin and earth as the tails into the main switch, so I can only assume their is a submain but my issue is the garage it's choca and we think it's where the main fuse is, would anyone be happy to put lim in this situation with the fuse ect/submain , as I am only from the house db adding circuits?

As in I can't put any details in as the main switch or submain board..can this be lims as I can't get to any of this?

Sent from my SM-G930F using Tapatalk

No, you cannot enter 'lim' into any part of an EIC, that is only used on an EICR.
Without the details of the incoming supply how on earth did you assess its suitability and adequacy to serve the additional circuits?
 
Well how can you determine what fuse it is without taking the fuse out? Which your not aloud to do???

Sent from my SM-G930F using Tapatalk
 
Well how can you determine what fuse it is without taking the fuse out? Which your not aloud to do???

Sent from my SM-G930F using Tapatalk

Well do it quietly then! Or did you mean allowed?

If it's a 10mm T&E submarine the e there must be a switchfuse there somewhere feeding it, so why would you not be allowed to take it out and look at it?
There's more to it than just the fuse rating anyway, which I'm sure you already know, you need to determine the earthing system, tails size, confirm the size of the earthing conductor etc




Sent from my iPad using Tapatalk
 
Also the circuits are new replacement to what was there already.

Sent from my SM-G930F using Tapatalk

That doesn't change the rules, LIM is still not an available option for an EIC! The only options are pass or not applicable, you cannot have a fail, limitation, further investigation or not verified on an EIC


Sent from my iPad using Tapatalk
 
That doesn't change the rules, LIM is still not an available option for an EIC! The only options are pass or not applicable, you cannot have a fail, limitation, further investigation or not verified on an EIC


Sent from my iPad using Tapatalk

I quite often bow down to your, and some other knowledgeable posters, wisdom on here Dave. But slightly sort of disagree with your post above. I recently came across a poor TNS earth connection which the DNO was promptly informed about. They came out within an hour, and stated that as all ccts were now RCD protected, it was not an emergency, and they needed a jointer anyway as they are going to have to dig outside. Personally I thought the sheath looked pretty good for renewal of the TNS, but what do I know! With a pair of long nosed gently holding the DNO clamp in place the Ze was good ~ 0.4 ohms or so. Without the long nosed it was around 70 ohms due to the loose clamp.

I thought the DNOs response was a bad one, and was not happy with it so I put in a temporary rod to get a high, but at least stable earth path.

On the EIC I did not put NA down in the earthing arrangements section, instead I made a note to refer to the comments on existing installation section as I felt it was relevant. Yes it could have been simply mentioned in a cover note (and it was) but felt a mention on the EIC was OK too.

OK, what I did may bit follow guidelines strictly, but I can live with it!
 
I thought it was the schedule of inspections for initial verification that you was only allowed a tick or n/a. Not verified would go on condition report inspection schedule.

Sent from my SM-G361F using Tapatalk
 
That doesn't change the rules, LIM is still not an available option for an EIC! The only options are pass or not applicable, you cannot have a fail, limitation, further investigation or not verified on an EIC


Sent from my iPad using Tapatalk
So if you can't see what you out for main fuse? Not applicable ?

Sent from my SM-G930F using Tapatalk
 
It's always applicable as far as I'm aware because as already stated you need to know ifthe existing installation is adequate for the new circuit.

Sent from my SM-G361F using Tapatalk
 
I quite often bow down to your, and some other knowledgeable posters, wisdom on here Dave. But slightly sort of disagree with your post above. I recently came across a poor TNS earth connection which the DNO was promptly informed about. They came out within an hour, and stated that as all ccts were now RCD protected, it was not an emergency, and they needed a jointer anyway as they are going to have to dig outside. Personally I thought the sheath looked pretty good for renewal of the TNS, but what do I know! With a pair of long nosed gently holding the DNO clamp in place the Ze was good ~ 0.4 ohms or so. Without the long nosed it was around 70 ohms due to the loose clamp.

I thought the DNOs response was a bad one, and was not happy with it so I put in a temporary rod to get a high, but at least stable earth path.

On the EIC I did not put NA down in the earthing arrangements section, instead I made a note to refer to the comments on existing installation section as I felt it was relevant. Yes it could have been simply mentioned in a cover note (and it was) but felt a mention on the EIC was OK too.

OK, what I did may bit follow guidelines strictly, but I can live with it!

I had one similar to that a few years ago , it was sparking under test.
I called the DNO (probably the same as yours.)they were there within half an hour and fitted a constant pressure clamp. Just a difference in people lol.
 

Reply to New circuits. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
890
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
646
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
837
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
270
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock