first fault is a cross connection between the upstairs socker rfc and the disused immersion heater radial, so the upstairs sockets get fed from 2 separate MCBs. this I will need to trace out after moving loads of itchy-poo.

2nd fault is the diabolical installation of the security lights. cpc's sleeved and used as switched L's on 3 cables. metal floodlights not earthed. no RCD protection on installation. I have disconnected for obvious reasons. Paul has requested a quote to rewire the security lights with new LED floods and PIRs, and to sort out the X-connection.
 
as in.......

upload_2017-7-13_15-41-18.jpeg
 
Can't you go and do a Ze your self as it might be that they just measured or wrote down incorrectly. As stated in a previous post what is wrote down for the prospective fault current?
 
Strange to not comment on it, but if all circuits have rcd protection, is that reading even a problem? Although if I measured that value then I'd still get the dno out for an unreliable earth, in case it gets worse.
 
Strange to not comment on it, but if all circuits have rcd protection, is that reading even a problem? Although if I measured that value then I'd still get the dno out for an unreliable earth, in case it gets worse.
Hi - the 2 Ohms may be ok if the installation is designed for that, as you would for a TT. But in summary - ask owner to call DNO and request a safety inspection (free) as they've been told by an Electrician that it may be unsafe. My concern is it may indicate a deteriorating condition and Client could end up with no earth. Apologies to all who've already said this on the thread, or if you've already established it's 0.2 Ohms :rolleyes: . Must have coffee ...
 
Hi - the 2 Ohms may be ok if the installation is designed for that, as you would for a TT. But in summary - ask owner to call DNO and request a safety inspection (free) as they've been told by an Electrician that it may be unsafe. My concern is it may indicate a deteriorating condition and Client could end up with no earth. Apologies to all who've already said this on the thread, or if you've already established it's 0.2 Ohms :rolleyes: . Must have coffee ...

yeah, a bit early for beer. just add a splash of scotch to the coffee.
 

Reply to New Member with an EICR question on max Ze reading in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock