Discuss new washing machine trips rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I

ian1511

washing machine trips rcd when turned on or off? this is on a newly installed ring on a recent job.as work had all been tested and no problems, job signed off and walked away. machine was 5-6years old recommended they get it looked at by an engineer, but they instead bought a new one.this still trips rcd when turned on or off.i have since been back and tried to pinpoint what is causing this but have hit a brick wall.it is only a washing machine that causes this have had dryer,extractor,undercabinet lights,2kw oil filled radiator,hoover,power tools,used on circuit and no problems.any one got any thoughts,thanks.
 
This might be a silly question but did you "PAT" test the washing machine the reason I ask is I had a problem like this when the customer switched the WM on via the FCU above the worktop I tested the WM and it was fine so before I started to scratch my head I tested the socket fed off the FCU and found the problem was that the screw had nicked the neutral behind the socket
 
i pat tested there old machine and it did pass leakage was little high but pass.i have retested all my work and changed over face plates in case one was faulty, everything fine.customer can be hard work and didnt believe me so i by-passed all my work and ran a brand new extension lead and hard wired to mcb.this still trips rcd when turned on or off.have ramp tested rcd and also fine.
 
ramp test trips at 26mA, there is also a cooker cct and lighting cct fed from this rcd db and everything can be on including all other appliances, only when a wm is used this problem occurs.
 
which would incline to me its taking it over the limit... stick washing machine on rcbo or separate rcd or wire it in fp200 type cable... hopefuly jobs a gooden
 
I had this about 6 months ago sparks was called re RCD tripping, all tested out fine,,but would trip when W/M used they had brought a new W/M and it still tripped,, I was called and tested everthing. full load kettle, tumbledryer, shower all on together no trip! I/R all >200M ohm. I did a timmer test and at x1 the RCD was tripping at 7ms.. I thought this was quick but dismissed it as everything else worked and didnt cause tripping, I also thought W/M. But just as a last ditch effort swoped over the RCD.. new RCD time 36ms@ x1 and now no W/M tripping!! hope this helps....
 
Last edited by a moderator:
wm trips rcd when nothing else is connected to the cct, i' am going to replace rcd on friday to see if this helps even though all tests seem fine and then after that have no more ideas.even if i try and pull in new cct i think problem will remain as i tried this with extension like mentioned before.
 
Does the washing machine still trip the RCD when plugged into another socket ? Use an extension cord to try it elsewhere.

If there's another house ring, then does it trip the RCD in that circuit too?
 
plugged wm into cooker point via extension and it tripped rcd, the cooker is a 5kw and been working fine at full whack since job was finished. rest of house isnt protected by rcd so they are currently running a lead from front room so they can use there wm.
 
To take a punt, I think changing your RCD could well clear the problem. I hate to say it, but it might just be one of those things!
 
Sounds to me like you'll need to get down and dirty and localise the fault within the washing machine with your mega tester. I've had earth leakage faults that were caused by the noise supression filters on an appliance and they only showed a fault with a mega tester when using 250volts test voltage and not at 500 or 1000 volts. At 250 volts it read approx 1.5meg ohm but at 500v it read >15 meg ohms. I have a very old analogue tester that has a 200volt mega test and that showed a reading of 0.2 megaohms.
 
Sounds to me like you'll need to get down and dirty and localise the fault within the washing machine with your mega tester. I've had earth leakage faults that were caused by the noise supression filters on an appliance and they only showed a fault with a mega tester when using 250volts test voltage and not at 500 or 1000 volts. At 250 volts it read approx 1.5meg ohm but at 500v it read >15 meg ohms. I have a very old analogue tester that has a 200volt mega test and that showed a reading of 0.2 megaohms.


This is just one of the very good reasons, why most modern high end IR testers and MFT's have 100/250/500/1000 volt ranges... Sometimes less is better for realistic or accurate values!! lol!!!
 
changed rcd today and it held,thank god.very unusal but at least its now sorted and i no if i ever cross this type of problem again.
 

Reply to new washing machine trips rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
581
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock