DB not connected directly to the main supply.
The confusing bit, characteristics at this DB, is this still related to the Distribution circuit.
You can actually read it both ways, I’ve been entering the Distribution circuit but now have my doubts.75F9686E-7EA8-4BD6-A0E4-2DAE14CC9087.jpeg
 
You've been doing it right. It's the Zs and PFC of the distribution circuit as measured at far end (the sub-main consumer unit)
This then gives you the base-line if you want to fabricate calculate Zs readings from the R1+R2 readings of the final circuits.
 
It's self explanatory. You're selecting an existing DB, then a sub DB, then entering the details for the sub DB and then the test results at it.
A distribution circuit is feeding the sub and needs listing as an out going circuit from the main DB.
Hope it helps.
 
Last edited:

Reply to Niceic certification in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
500
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Not sure whether this is the right context or even forum to mention this, but I’ve recently been offering out myself to a friend to help get his...
Replies
7
Views
402
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
478
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
580

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock