Apparently if the pipe work in a property achieves certain resistance there is no need for bonding if a RCD is used. What is the figure that needs to be achieved? I have been looking through the regs this morning but haven't found it.
 
Last edited by a moderator:
Apparently if the pipe work in a property achieves certain resistance there is no need for bonding if a RCD is used. What is the figure that needs to be achieved? I have been looking through the regs this morning but haven't found it.

If im correct in saying, 7666 Ohms is the maximum resistance allowed. I did: V/I = R 230/0.030 (30mA) = 7666 Ohms.
So long as the resistance is below this reading, the RCD should trip according to plan. Thats why we use them on TT systems a lot, because of the high resistance readings that could occur, and the 7666 ohms is lets face it - pretty high....

Other comments would also be appreciated so i know if im on the right lines.

Hope this helps anway.
Dan...
 
I thought the level given in the regs was 1667 ohms? Can't check as it's beneath a pile of stuff at the moment and I'm not brave enough to start disturbing it.

If I recall rightly, a voltage of maximum 50V with a current of 30mA is considered to be below shock levels, and so this should be the maximum value permitted when an RCD is used. R=V/I would then be: R=50/0.03, so R=1667 if rounded up from 1666.666-recurring. If the resistance was higher, a higher voltage would be required and as such the 50V limit is exceeded and values are above those deemed enough to cause a shock.
 
Last edited by a moderator:
Correct Chappers, 50V is the "safe touch voltage" hence the calc R=50/0.03=1667ohms. which is maximum permissable Ra or (Ze) for a "TT" system although 200ohms is generally regarded as the maximum acceptable before you need to do something about it.

Cheers.
 
Thanks, forgive me if this is a daft question but all the replies so far seem to be concerning a TT installation. Would the same formula apply to TNS etc? I just want to make sure I fully understand.

Paul
 
Hey mate.

That calc is for the maximum permissible Ze with the "safe touch voltage" in order to hit your disconnection times for 30mA RCD's

With respect to TN-C-S it's max Ze of - 0.35ohms
TN-S it's max Ze of - 0.80ohms

Cheers.
 

Reply to No bonding with RCD in the Australia area at ElectriciansForums.net

Similar Threads

Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
256
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
424
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
929
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock