Search the forum,

Discuss No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Iona222

Trainee
Reaction score
41
Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.

The cooker sockets is working also.
 
Neon on switch between L and N?
also, what continuity test are you doing?
 
What reading are you getting. You will only get a line to cpc reading if you have connected a link across them.
 
Not getting a continuity reading on the cooker circuit. I'm doing I.r. test and its low between l. N. Any ideas what the issue could be.

The cooker sockets is working also.
What exactly do you mean by not getting a continuity reading? how low was the IR Test? cooker sockets is working also?
 
Dont want batter you with too many questions but as above can you clarify. Insulation resistance test at 500v or continuity test.
 
I have mate. I'm not getting a reading. When I link line and neutral I get 0.10 ohms

So there must be a break in either the live or the earth. Now, along with the line-to-neutral being OK, you say the socket is working so those may be a clue.

I bet Zs is poor. Although obviously dead tests should be sorted first.
 
Last edited:
This is a matter of deduction, three conductors and two linked are fine but the third when linked is not so what does this tell you.
 
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work

Sound mate.
 
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work

Sound mate.
Test cont between LN LE NE IR the same and publish the results,
 
Are you linking out at the CU and then testing at the cooker isolator or the connector plate lower down? Make sure you are breaking it down correctly. Test just the feed cable (unless that's what your having issues with...) then just the cable from the switch to the connector plate. This will rule out bad connections.

If you are testing with the switch inline and it's not been used before (brand new) make sure you rule out a faulty accessory
 
Last edited:
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.

Ah sorry. You've got a trainee badge on your status so assumed you were still learning. Obviously wouldn't be doing EICRs if you were. Be worth getting the mods to remove that if that's the case.
 
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.
Fear not it does get easier.
If it's an EICR I'd probably have started with a Zs test using the socket on the cooker plate. In under a minute you'd know you have a CPC issue, either broken or termination issue.
 
Simple one point radial circuits assuming that is what it is are straightforward to fault find and once you achieve this it will give you insight to something more complex, but complex or not fault finding methods are generally the same.
I'm rubbish at fault finding mate, suppose improve with experience.
 
You need to visualise the circuit and a drawing helps. With the type of circuit you have this is straightforward if I remember tomorrow I will do some rubbish? drawings.

Westy is spot on here. Draw the circuit. Work out why you get the readings you get. It's not difficult- don't over think it.
 
Its just a cooker circut , pal, im thinking the earth cable is damaged.
You need to prove this so draw three lines, line, neutral and cpc. Leave the cpc with a gap in it and decide how continuity tests will prove the cpc is broken. You have a continuity tester and a lead with croc clips either end.
 

Reply to No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
438
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
859
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
288
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
859
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top