Search the forum,

Discuss No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work

Sound mate.
 
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work

Sound mate.
Test cont between LN LE NE IR the same and publish the results,
 
Are you linking out at the CU and then testing at the cooker isolator or the connector plate lower down? Make sure you are breaking it down correctly. Test just the feed cable (unless that's what your having issues with...) then just the cable from the switch to the connector plate. This will rule out bad connections.

If you are testing with the switch inline and it's not been used before (brand new) make sure you rule out a faulty accessory
 
Last edited:
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.

Ah sorry. You've got a trainee badge on your status so assumed you were still learning. Obviously wouldn't be doing EICRs if you were. Be worth getting the mods to remove that if that's the case.
 
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.
Fear not it does get easier.
If it's an EICR I'd probably have started with a Zs test using the socket on the cooker plate. In under a minute you'd know you have a CPC issue, either broken or termination issue.
 

Reply to No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock