Discuss No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net
Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.
So the means of fault protection wouldn't function then. Additional protection might. But issue needs solving.But everything fine apart from no continuity on the line earth at cooker.
Test cont between LN LE NE IR the same and publish the results,Zs for the installion is OK. But everything fine apart from no continuity on the line earth at cooker. Obviously if there's a fault the breaker might to work
Sound mate.
Ah - as he said it was 'working' I assumed it wasn't initial which may have been the wrong conclusion.If this is an initial verification do not energise the circuit for a Zs until this is resolved.
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.Zs won't be fine on the cooker circuit I bet.
So, what is the next step you will make?
Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.
Fear not it does get easier.Tell the client the have a fault. They need to get fixed. I'm just doing the eicr. I'm rubbish at fault finding mate.
Reply to No continuity on cooker circuit. in the UK Electrical Forum area at ElectriciansForums.net