Discuss No CPC’s, conduit doing it’s job, C2 or C3? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
I’ve just done an EICR on an old 2 bed flat that is wired in all metal conduit wired in singles however there are no CPC’s. The conduits are all bushed into the old rewireable board and back boxes/conduit boxes for lights and I’m getting good Zs readings at all outlets through the sockets/lights being fixed into the back boxes/ conduit boxes. There are no fly leads from the boxes to the cpc terminal on any of the sockets/fittings as there are no fixed terminals on the back boxes due to their age. All bonding is in place and I will be upgrading the consumer unit to a new RCBO board. I’m considering putting the fact their are no CPC’s down as a C3 rather than a C2 as it was obviously compliant at the time and I’m achieving compliant Zs readings. Thoughts?
 
What are you questioning no cpcs to the accessory front plates or no cpcs through the conduits.
 
With power accessories such as socket and fuse connection outlets the cpc is important as would metal be for metal plated light switches but you have to make a judgement as to how detrimental their absence is. How are the light fittings connected to the conduit system.
 

Reply to No CPC’s, conduit doing it’s job, C2 or C3? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hi all, I'm wondering if it's permitted to replace an outside wall light myself if I use the existing wiring from the old light. In theory I just...
Replies
2
Views
645
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock