Search the forum,

Discuss no earth in the UK Electrical Forum area at ElectriciansForums.net

Stroppy, if you're that close to your local tranny, fit an MET in your house, then run a 16mm cable from it to said transformer and bolt your cable onto it. Cover it over with dead leaves and other general detritus.
Should give you the best Ze in the area.

Don't forget the rated breaking capacity of your equipment is only 6KA though... ;)
 
Stroppy, if you're that close to your local tranny, fit an MET in your house, then run a 16mm cable from it to said transformer and bolt your cable onto it. Cover it over with dead leaves and other general detritus.
Should give you the best Ze in the area.
or the nearest lamppost....just wrap it round...a bit of a twist to get it tight....
 
My gas pipe is definitely straight in the ground, as I can see it - its an ancient iron/steel thing that disappears into the earth. Anyway, I disconnected the bond from the gas pipe and still got 0.46, but then it ocurred to me: as the pipe is connected to appliances which have their metalwork earthed, am I not getting a parallel path through their CPC's? I'm not going to the trouble of disconnecting those, or the bonds on the water pipe or central heating as they are under the floor and a pain in the arse to get to. I'm getting more confused about this by the minute!

The more I think about it I think it is the gas service, as (a) it is a metal pipe going straight into the ground, and (b) the gas-main in the road goes right past the transformer within about 2 metres of it.

Testing the MET without the twig got me 0.35.

May be you can, but if it's iron pipe it will definitely have a wrap below ground (Used to be a grease impregnated tape, which i can't remember the name of at the moment). What you can see, is where it hasn't been properly wrapped after up-stand connection by the original gas fitters. The same will go for the copper pipe, that probably been tee'd of an old main line lead wrapped pipe.

Far more likely that a neighbour or neighbours have had a PME upgrade, and your seeing the results from the bonded services from those properties!!. But you have to remember that your metal service connections, are bonds (as they are in the other properties) and not a recognised earth electrode. So while it is improving your TT system to TN values, it's not really the best place to be!!
 
May be you can, but if it's iron pipe it will definitely have a wrap below ground (Used to be a grease impregnated tape, which i can't remember the name of at the moment). What you can see, is where it hasn't been properly wrapped after up-stand connection by the original gas fitters. The same will go for the copper pipe, that probably been tee'd of an old main line lead wrapped pipe.

Far more likely that a neighbour or neighbours have had a PME upgrade, and your seeing the results from the bonded services from those properties!!. But you have to remember that your metal service connections, are bonds (as they are in the other properties) and not a recognised earth electrode. So while it is improving your TT system to TN values, it's not really the best place to be!!

Denzo Tape maybe???

Not sure myself to be honest - it's just a name that's lurking in a dark corner of my mind.
 
I do realise that the services are not there to be used as an earth, and the difference between earthing and bonding, which is why I started all this: testing the effectiveness of my earth twig. I will see if I can get PME'd, which would be the better option, otherwise I'll get some chunky rods and start driving them into the mud-bath that is my garden.

One day I'll get under the floor and individually test all the pipework and find which one is the culprit, but for now I CBA!
 
Denzo Tape maybe???

Not sure myself to be honest - it's just a name that's lurking in a dark corner of my mind.

Yes, that sounds about right!! lol!! As others say, really horrible stuff to work with, but it works. Must have been around now for 60 odd years or so now, under various names and variations etc!! lol!!
 
Yes, that sounds about right!! lol!! As others say, really horrible stuff to work with, but it works. Must have been around now for 60 odd years or so now, under various names and variations etc!! lol!!

Oh yes it works very well.

I remember my Dad making some clothes posts for my Mum to tie her washing lines to. He made them out of steel pipe that he nicked from work and he wrapped the lower part that was going to be buried with Denzo.

That was in 1950 something and those posts were still there in 2008. That's the year when Mum died and I sold the house, so they're probably still there for all I know.
 
Ofcourse, as a temp measure a water main is much more reliable than dodgy reading Ra on an electrode, however it could be replaced with plastic, so any pemenent matalic stucture that is soundly connected to earth and in your opinion doesnt deteriorate is acceptable as a reliable earth in aTT system.

I must admit that if any upgrading to the water system took place where the old lead water mains was cut off in the road you would still have anything up to 30m of buried lead pipe in the ground.
This now being obsolete would make a very nice 'twigg' and then on used as the earth electrode for the installation. One would assume that RCDs/RCBOs were in place if the Ra was too high.........

I've just managed to get a front row seat - you can stuff the pop corn !
 
I must admit that if any upgrading to the water system took place where the old lead water mains was cut off in the road you would still have anything up to 30m of buried lead pipe in the ground.
This now being obsolete would make a very nice 'twigg' and then on used as the earth electrode for the installation. One would assume that RCDs/RCBOs were in place if the Ra was too high.........

I've just managed to get a front row seat - you can stuff the pop corn !
same goes for private services (boreholes)...if you can ensure there will be no `upgrades` or tampering etc...
 
I must admit that if any upgrading to the water system took place where the old lead water mains was cut off in the road you would still have anything up to 30m of buried lead pipe in the ground.
This now being obsolete would make a very nice 'twigg' and then on used as the earth electrode for the installation. One would assume that RCDs/RCBOs were in place if the Ra was too high.........

I've just managed to get a front row seat - you can stuff the pop corn !

Wouldn't be up to much as an earth electrode, Just a typical extraneous service value, unless you stripped all the protective wrapping off of it!! ...lol!!
 
Wouldn't be up to much as an earth electrode, Just a typical extraneous service value, unless you stripped all the protective wrapping off of it!! ...lol!!
and theres nothing to day that in future the path isn`t dug up...and that 30 meters all of a sudden becomes about 3-4...lol...
you just cant rely on it...
 
is that `sticky toffee pudding` then ack?...

Lol, I just looked up the H&S requirements for this stuff and as suspected nothing to report, just use a bucket load of swafega and hot water. However, it is suggested that if ingested you should seek medical advice ?!!!.

I never considered that there might be any nutritional value in the gunky cloth/tape !
 
nah, tony's star/delta with a squirrel cage.

TonyCage.jpg

........
 
dig the garden then

Its going to down about metre so unless you're putting in the foundations for an extension then its unlikely to be affected. A loop measurement or better still, run your test electrodes across the lawn and into the next doors garden to get a resistance would be sufficient.

Alternatively use the exploration hole to wack in a 'twigg' and back fill with bentonite - Job done - lol
 
I do realise that the services are not there to be used as an earth, and the difference between earthing and bonding, which is why I started all this: testing the effectiveness of my earth twig. I will see if I can get PME'd, which would be the better option, otherwise I'll get some chunky rods and start driving them into the mud-bath that is my garden.

One day I'll get under the floor and individually test all the pipework and find which one is the culprit, but for now I CBA!

Regular viewers may remember this discussion about my pitiful 125 ohm reading from my earth rod (and unbelievably low Ze through the bonding). I know it is nice to have follow-up on discussions, so let's put this one to bed:

This afternoon I finished work at lunchtime and as, for once, it is not raining I thought I would sort out my earthing before I got cleaned up for the weekend. I have now pulled out my old 'twig' and pounded in two of Sarnia Electrical's finest shiny 3/8" earth rods and connected up my earthing conductor. Now I have a much more reasonable Ze of 44 ohms and a fault current of a whopping 5 amps.

That will do! As my late wife said, deeper is definitely better. :)
 

Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
575
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock