Discuss No earthing on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

There’s a requirement to provide labelling at the DB for circuits with high protective conductor currents but no such label exists in bs7671 so it’s a similar situation label wise I mean.
The label for protective currents above 10mA is required by bs7671 in section 543 and is mentioned so perhaps that is indeed the big difference between the 2.
Often labels required are not actually in the wiring regulations themselves.
OK, but the fact remains that not having a cpc terminated at every point in the wiring is not permitted by BS7671 for an ADS system.
 
What you should do is provide RCD protection along with plastic accessories and the label.

Agreed, I was going to raise that. Given the suspected age of the installation I would suspect that there is no RCD protection. I would want that, for a rented property, on the sockets at least.
 
Agreed, I was going to raise that. Given the suspected age of the installation I would suspect that there is no RCD protection. I would want that, for a rented property, on the sockets at least.

It shouldn't really make a difference as far as RCD protection if the person has bought or is renting the house. But I know what you mean.
 
Thanks for all your helpful advice.
Just to clarify to the last few posts regarding RCD protection, I was planning on replacing the CU and ALL circuits would have RCD protection.
I would not be altering any cables in any circuits, just replacing accessories.
Also, I planned to replace all switches with plastic ones and use the push in plastic screw covers usually supplied with them, also all switches would be mounted on plastic surface backboxes to maintain the best insulation I can.
On a similar note, i'm surprised that they don't make labels to mount on/near the CU to warn of no earthing on lighting circuits, as i'm sure this is a common issue in very old properties. I'm assuming its just a case of getting the labelling machine out and typing something to that effect.
 
I stand corrected on my last post, turns out they do make "no provision for earth" labels. I just ordered some. I should have checked before sending post, oops.

WarningNoProvisionBS7671.jpg
 
Hi all, I've been asked to make an old 4 story townhouse "safe" and issue cert for renting out.
Hasn't been touched for so long it has bakerlite accessories with wood backing!
Straight away I'm seeing replace all accessories, replace CU, upgrade earthing. The wiring is all in PVC cables but typical no earthing on lighting circuits.
I hear you all scream "REWIRE"!
Problem is property is highly decorated and furnished and owners would rather not go down that route.
My question is, if I fit all plastic accessories throughout, and clearly state on CU and cert NOT to fit any metallic fittings. Can I get away with that?
Just asking as whenever I've come across this problem in past, I've always rewired lighting so bit unsure what complies.
By the way, I've done quick IR, ring loop tests, Ze etc and all ok, but how do you R1+R2 lighting with no earth?
Personally I would be advising that if you want it making safe then there is going to be some rewiring needed,the place may be decorated but that's not your problem, you have been asked to make it safe and I wouldn't feel like I have made it safe by installing fittings with no earth.
 
Maybe the printer had a lisp ?
Should that be 'lishp'?

Had a situation a while ago, I think I mentioned it on here, where I changed a CU for a friend. Wiring to one light under the stairs (I put it on it's own cct) had no earth. I showed the NIC inspector and he agreed it was OK, with appropriate label.
 
Last edited:

Reply to No earthing on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
864
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock