J

jase31

Problem with meter / distribution board. All electric has gone off. Electronic Prepayment Meter. Power going into meter. When distribution board is OFF then there is power from the meter to the board. The moment a load is applied there is no power from the meter to the distribution board. I have switch each circuit off in turn, and the moment any 1 circuit is on then no power flow from Meter to Dist board. Am I right in thinking this is the meter?
Edit
 
Have called DNO twice, and on both times told (over the telephone) that it is not a meter fault. How can the power flow from the meter to the fuseboard stop whenever there is a load applied - unless it is a fault with the meter. Is there anything else I should check for?
 
how are you testing for the presence of power?
 
if you are competent to do it, multimeter across L/N on incoming side of main switch. repeat for L/E both with and without load. if you lose either L or N then it's deffo a DNO problem. what's your location.? maybe one of us is close to you.
 
It could be a connection breaking down on the supply either external to the property or a tail connection. It is possible to have a bad connection in the meter as it is a pre pay and they have some sort of contact that makes and breaks depending wether the meter is in credit or debit. Are you sure there is credit on the meter??? A loop test each side of the meter will soon sort it out. Multimeter will pick up any voltage where as a loop tester will load the circuit and pinpoint the fault.
As the other say get the DNO out. Dont tell them it is the meter just say you are off supply, they will be out within 4 hours.
 
Last edited:
Multimeter on. Distribution board off. L/N 111v L/E=111v When any load is applied voltage drops to 0.

Putting the multimeter on the meter tails, 238v on the input tails, and 111v out, again drops to when any load applied. DNO insist that it is a house wiring fault and they are not responsible as the meter is illuminated at displays 88888888 when the blue button is pressed.
 
Last edited by a moderator:
its a dno fault quite possibly breakdown of service fuse seen it before although it could be a line problem, check tails at your end if ok call dno with a off supply that will get the guys round who will fix it.
 
If its a prepay meter with a plastic key make sure that the credit is on the meter correctly.

Had a simular one where it was showing ÂŁ15 in credit which had just been put on but no power took the key out and reinserted it pressing various buttons and it powered up straight away.
 
neon tester ??????????????????????? good grief is this a joke.
First of all test with a multimeter if it is a prepaid meter dont use a standard mains tester unless you are testing L-N only if you test L-E with one of these the meter cuts out.
 
its a dno fault quite possibly breakdown of service fuse seen it before although it could be a line problem, check tails at your end if ok call dno with a off supply that will get the guys round who will fix it.

Thanks. Have called DNO (Central Networks) who then claim as the meter is illuminated (hence there is power to the meter) it is not their responsibilty and I need to call the electric provider (british gas) who are responsible for the meter (and who only answer the phone 8am-8pm)
 
Last edited by a moderator:
DNO will not respond if the meter is lit. It does sound like it could be a meter problem. (does the incoming voltage drop off when a load is applied) You need to call the people who supply your electricity ie who you pay your bill to (prepay) They are responsible for the meter. It may still be E. on but a different department. You can find out who your electricity supplier is by contacting your local electricity distribution company . You should ask for their Meter Point Administration Service (MPAS).
 
The old days were better one electricity company to deal with. Now we have the DNO for the supply and cut off then the suppliers meter operator for the meter.

Let us know the outcome
 

Reply to No power from meter? Is this meter or wiring fault? in the Australia area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
549
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
461
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
234
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
401

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock