Discuss Noisy RCD. - BG brand in the UK Electrical Forum area at ElectriciansForums.net

1Justin

-
Arms
Reaction score
157
I thought I'd try a BG CU.

The RCD's are noisy under load. Perhaps 2KW sets them off, a buzz which is quite audible from a few feet away. I swapped the noisy RCD for the second (since that side was still unused when I worked this out), the other one is also noisy, but less so.

Both switch fine, measure up (disconnect) fine, Zs fine, and no signs of anything wrong, no smell, heat etc. - Just the noise.

Is this normal for a BG brand RCD? Does anyone have anything to offer, or should I take them back?
 
could be a fault on the circuit. i fit BG regularly and ain't never herd them buzz, but then again, i'm a bitt mutton, so who knows? at least they not got recalls.
 
All connections are tight. I checked that already, but I will re-check since all the screws on thes BG (on the MCB's and the N E bar) are very stiff.
The load(s) which cause it may well be a bit inductive, because it's the heavy (heating) loads - eg kettle.
No dimmers.
Circuit all measures OK

The buzz under load is low level, but noticeable in quiet space.

It sounds like slight 50Hz rattle - like you might get from a loose winding of a transformer.

Just had an idea, I could pop the RCD into my own CU to try it, maybe worth a go.
 
All connections are tight. I checked that already, but I will re-check since all the screws on thes BG (on the MCB's and the N E bar) are very stiff.
The load(s) which cause it may well be a bit inductive, because it's the heavy (heating) loads - eg kettle.
No dimmers.
Circuit all measures OK

The buzz under load is low level, but noticeable in quiet space.

It sounds like slight 50Hz rattle - like you might get from a loose winding of a transformer.

Just had an idea, I could pop the RCD into my own CU to try it, maybe worth a go.
are you sure about this statement justin?
 
Hi Glenn,

Well I don't know, but a kettle is heated with a ceramic wire coil. Not exactly a motor winding I know, but it's not going to be a pure resistor. Anyhow, clutching at straws here since Chopper posed the question.

"Clamping all the tails together?" I'm not with you on that one.
 
Hi Glenn,

Well I don't know, but a kettle is heated with a ceramic wire coil. Not exactly a motor winding I know, but it's not going to be a pure resistor. Anyhow, clutching at straws here since Chopper posed the question.

"Clamping all the tails together?" I'm not with you on that one.
clamp both the tails with a leakage clamp....any mA shown will be the leakage...i suspect those RCDs are near their limit....
 
It may be it's close to the tripping threshold or it may be there's something wrong with them. To be honest if there's no problems with the circuits I'd return them to the wholesaler for a warranty and get them to investigate the issue, bottom line is they shouldn't make a noise and the customer will probably complain sooner or later.
 
Hi Glenn, Hmm leakage. Firstly might a standing leak show up as significant offset in the break time between positive and negative cycles? (I see no big difference).

& Insulation resistance is very high.

I also don't have a current clamp - maybe I should have one, would be handy from time to time. Thanks.
 
It may be it's close to the tripping threshold or it may be there's something wrong with them. To be honest if there's no problems with the circuits I'd return them to the wholesaler for a warranty and get them to investigate the issue, bottom line is they shouldn't make a noise and the customer will probably complain sooner or later.
well this was my initial thoughts here marv...

i will say this though Justin....a while back one of the counter staff at a screwfix up here in Leeds mentioned they`d had a lot of these british general boards back with issues about this n that....
 
Hi Glenn, Hmm leakage. Firstly might a standing leak show up as significant offset in the break time between positive and negative cycles? (I see no big difference).

& Insulation resistance is very high.

I also don't have a current clamp - maybe I should have one, would be handy from time to time. Thanks.
a requirement really when RCDs are about...the alternative is to ramp it off load...then again on load...the difference will be leakage....
 
Yep, I've just been looking up clamp meters on line, need one with good resolution down to mA and AC DC also.

I was unsure of the BG board in general, maybe not again..

Mechanically it's nice, better than MK. The front goes on really well and doesn't bend. (- Perhaps removing it is a tad too easy though with two quarter turn locks). The switches run right to left, but the earth bar is numbered left to right. - RCD is right to left so to speak, which means I couldn't try it out this evening in my own MK board since the busbar on wrong side.
 
Last edited:
Yep, I've just been looking up clamp meters on line, need one with good resolution down to mA and AC DC also.

I don't know how you're going to test the actual leakage without one. I would look at the Dilog earth leakage clamp, it's very reasonably priced and gets good reports but I'm not sure about it's DC capabilities.
 

Reply to Noisy RCD. - BG brand in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them...
Replies
1
Views
779
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all...
Replies
18
Views
2K
Doing standard tests prior to some minor works on a socket circuit (Zs, IR etc), pressed the test button on the RCD, tripped fine, got ready to...
Replies
3
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock