Discuss Non priority shower unit issue in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all, I have 2 showers running off a Garo Non priority unit. This causes one shower to not activate if the other is on.

1 of the showers is working fine. The other turns on for a few seconds & then loses power completely. I'm abroad so I've had an electrician look at it for me & he's saying the wire to it might be faulty. Am I right in saying this isn't a possibility from looking at the wiring diagram?

He's swapped connection from shower 1 to shower 2 on the contactors however the fault stays with the original shower.

wiring.png
 
I think the fault may also be with the 'original shower' or - inadequate water flow/pressure to it or flow from it, either causing the shower to trip on overheat.
 
I've had to deal with this before.


It turned out to be the contactor in the unit in the attic. That took a long time to diagnose considering I wasn't told that there were two showers from the one supply.


But considering your electrician is there, you have to trust his analysis.
 
Ok. Silly question time.
How does that circuit work?
It looks like you have the 40A feed for the shower going through the coils of K3 & K4 before it goes to the shower.
The 6A feed goes through the NC of K3 & K4 which energise K1 & K2
I'm presuming K1-K4 are contactors.
 
K3 and K4 sense the flow of current to each shower. When the current through their coil is greater than 11-12A their corresponding contacts open. Since K3's NC contacts are in series with contactor coil K2 and K4's NC contacts are in series with contactor K1......

I leave you to complete the explanation.
 
K3 and K4 sense the flow of current to each shower. When the current through their coil is greater than 11-12A their corresponding contacts open. Since K3's NC contacts are in series with contactor coil K2 and K4's NC contacts are in series with contactor K1......

I leave you to complete the explanation.

Thanks @marconi, that makes more sense.
 

Reply to Non priority shower unit issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

One of our contractors has identified a concern with multiple showers on a single 100 amp supply.(unsure how many yet i have asked for further...
Replies
3
Views
191
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
574
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
248
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock