Hi all
Went to a Newly Built Granny-Flat last week on behalf of MK's Switch Exchange Program
Opened the CU to find
  • spaghetti Junction,
  • No Labels,
  • Tails half out of Main Switch,
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat - (Don't know why 3)
  • No Bonding anywhere

Certificates:
  • No Property Name
  • Customer was the building company
  • Ze results mixed with Zs results
  • Non-Body Certs
  • No Signature on bottom of Certs

Gave the Electrician a call - details found in designer section only - asked for his registration number - reply "C&G 2382 and C&G 2391 I think!"

Asked for NAPIT, NICEIC, etc - reply what are they!

He recalls wiring the house - he didn't know he had to be registered


Called LABC - their reply:
  • No Building Control Certification
  • No Building Control Notice for Electrics
  • No Building Control Notice for Gas
  • No Building Control Notice for Insulation
  • No Building Control Notice for Windows
  • No Building Control Notice for ANYTHING!
  • Only thing they could find was Planning Permission which the customer applied for

Customer spent £85,000 for this build

Electrician is from Manchester Area - Worked down in Pembrokeshire, Wales on this one job
I don't know if I can post the name of the construction company or Electrician - MODs advise please
 
the building is subject to planning control anyway, so the electrician does not need to be with niceic, elecsa etc. as long as LABC are satisfied he's competent, all that's needed is for LABC to receive a copy of the EIC. as for the problems with the installation itself, that's another issue.
 
  • No Labels
  • Tails half out of Main Switch
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat
  • No Bonding anywhere

How are any of these complaint? - im sure I dont need to quote regs they dont comply with


Same goes for the EIC - Not worth the paper its written on!
 
  • No Labels
  • Tails half out of Main Switch
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat
  • No Bonding anywhere

How are any of these complaint? - im sure I dont need to quote regs they dont comply with


Same goes for the EIC - Not worth the paper its written on!

No labels- hardly going too do any harm to anyone is it
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
16mm SWA- What problem here?
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
PME- DNO responsibility? Although no problem with extending it
50 MCB- sounds like it is doing its job properly
3 showers- No problem here
No bonding- are there any extraneous conductive parts?

So aside from the top 2 pretty compliant so far unless you answer the questions I have asked
 
this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.
 
No labels- hardly going too do any harm to anyone is it
No RCD, Circuit Identification - not sure if a reg but good practice as these are included in the CU
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
Tails not in properly - and not cut tidy - only 3 cores connected!
16mm SWA- What problem here?
50m Run - Preferably 25mm would have been better to avoid voltage drop!
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
SWA Buried underground
PME- DNO responsibility? Although no problem with extending it
Regs State this must be TT
50 MCB- sounds like it is doing its job properly
RCD Discrimination
3 showers- No problem here
if 2 Showers Running - MCB Tripps - 4 Bedrooms for all family members - usual situation for this customer
No bonding- are there any extraneous conductive parts?
All Pipework is metal

Check your regs!

- - - Updated - - -

this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.

I know - didn't take one - wish I did though

- - - Updated - - -

Why has the original contractor not been asked to this if it's a new build?


Original contractor subbed it to this Electrician!
 
by my rough calc. 16mm will handle 46A over a 50m length, giving a VD of 3% . what's the problem?
 
So you are saying only 3 cores of the SWA connected into the switch?

Does the 16mm suffer volt drop outside of the permitted in BS7671

What regs for SWA buried has to have a earthed sheath? TT on a outhouse, all they have done is extended the PME zone. Perfectly acceptable. Have you proven the metal pipework is a extraneous conductive part?

Ok so bad design on the showers.
 
this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.

2013-11-19 23.15.15.jpg

It was very similar condition to this one just bigger - 21Way MK CU - Split Load


This picture is taken of one I attended for British Gas Home Assistance
 
Originally Posted by Dillb No labels- hardly going too do any harm to anyone is it
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
Tails not in properly - and not cut tidy - only 3 cores connected!
16mm SWA- What problem here?
50m Run - Preferably 25mm would have been better to avoid voltage drop! ....Better maybe, but that's not saying it doesn't comply!!
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
SWA Buried underground Is, or has the SWA been earthed at one end only ''outgoing end''??
PME- DNO responsibility? Although no problem with extending it
Regs State this must be TT .....REALLY THINK AGAIN!! Better still name that Reg?? lol!!
50 MCB- sounds like it is doing its job properly
RCD Discrimination ...Not actually against any regulation
3 showers- No problem here
if 2 Showers Running - MCB Tripps - 4 Bedrooms for all family members - usual situation for this customer .....Is this a Granny flat or a 4 bed house, ... make you're mind up??
No bonding- are there any extraneous conductive parts?
All Pipework is metal .....internal maybe, but what of the pipes entering the property, these day's plumbers tend to use plastic for everything??
 
So you are saying only 3 cores of the SWA connected into the switch?

Does the 16mm suffer volt drop outside of the permitted in BS7671

What regs for SWA buried has to have a earthed sheath? TT on a outhouse, all they have done is extended the PME zone. Perfectly acceptable. Have you proven the metal pipework is a extraneous conductive part?

Ok so bad design on the showers.

This building is 50m away from the main house! The Pipework is connected directly to a well!
You cant just extend a PME supply in this means - trying to find Reg now
 
trying to find Reg now

Best of luck, but you ain't gonna find one!! There is NOTHING wrong with extending a PME's Equipotential Zone. Distance vs cost being the main factor as to whether you leave the Superior earthing system behind in favour of a TT system....
 
One last time, i am repeating myself here. Is the metal work a extraneous conductive part? have you tested to prove it one way or the other?

Yes I have!

Ze between 100 and 200 ohms - acting as an earthrod


in regards to SWA - Armour is jsut cut and tapped at both ends - no glands
Inner insulation just passing through a 20mm hole in Iso in Main House - no supporting clamps - no earthing clamps
In House SWA is cut - only earth Conductor over 10mm is the 3rd core of SWA


2 x 30mA RCDs in Series
 
So you livened the house up without the main earth being connected?

What was your IR result when you tested between the main incoming earth and the metal work?

- - - Updated - - -

Yo have left lots of information out of you OP.
 
So you livened the house up without the main earth being connected?

What was your IR result when you tested between the main incoming earth and the metal work?

- - - Updated - - -

Yo have left lots of information out of you OP.


Like I said I went in to change Main Switch
Main Earth is connected via 3rd Core in SWA - its the Armor at Fault
Didn't IR - Installation Isolated and advised to get an electrician to repair work

Part of the MK contract is Im not allowed to offer my services to do work for these customers

Property owner is a retired Electrician (15th Regs) he had not looked in the CU ever
Nor had he checked any work - he relied on the Electrician being qualified and registered

I know i left lots out on my OP - sorry

Wish I had taken Pictures now! - Hind Sight is wonderful

- - - Updated - - -

I have a feeling the OP may have been registered before under a different name.

Never only this name sorry to disappoint you Dillb
 
Like I said he is a retired electrician - Even he was discussed with the quality of work
He agreed to Isolation


Napit, MK and LABC also Advised Isolation until it had been fully tested by a qualified electrician
 
This thread is so full of cattle excrement its unbelieveable

You were changing the main switch, you had no idea why the original contractor didn't do it. Then you are working for MK. How do MK know his main switch need changing. Also while you were there you have spent a good amount of time examining the installation even though your job should have taken about 10 minutes?
 
This thread is so full of cattle excrement its unbelieveable

You were changing the main switch, you had no idea why the original contractor didn't do it. Then you are working for MK. How do MK know his main switch need changing. Also while you were there you have spent a good amount of time examining the installation even though your job should have taken about 10 minutes?

MK had a recall on several Main Switches - Main Contractor stated he could not attend so MK Passed it onto myself!

Look i don't need to explain myself to you - yes I should of taken a picture and maybe you would have seen.

I have a very good reputation in this end of the woods - Working for several very large names including the ones mentioned in this thread and many others.


I only posted this as a good conversation - yes I should of said more in the OP

Lets put this thread to lay because at the moment Dillb you are only obsessed in having a bitch like always!

END OF!
 
View attachment 21871

It was very similar condition to this one just bigger - 21Way MK CU - Split Load


This picture is taken of one I attended for British Gas Home Assistance



looked at that. decided no more beer today. then looked again, decided beer not to blame.
 
bloody showers.. invention of satan. how the hell can you enjoy a single malt and a smoke in a bleeding rainstorm. give me a jacuzzi bath any time.
 
I'm REALLY curious as to why so many think you can't extend an equipotential zone on a PME install.....
Wholesalers must love the ability sell all those extra earthing rods....

Its a thing from the 80's along with staking down gas meters and plastic isolation valves on outside taps.

It funny how thing are dangerous and then not. Don't you love regs
 
Its a thing from the 80's along with staking down gas meters and plastic isolation valves on outside taps.

It funny how thing are dangerous and then not. Don't you love regs

Nope, it's down to the pure ''Scaremongering'' being perpetuated by the few still out there, that consider the PME artificial earth, as being an earthing system that is ready to kill each and everyone that has it installed!!

These herberts would rather see a TT system with crazy Ra values. There is one such guy on another forum, that has actually disconnected a perfectly sound TN-S connection for a 50 ohm TT system!!! Why because he believes that his TN-S DNO cable may have in part, been converted to TNC-S... lol!! There's nought so strange as folk, as they say!!
 
MK had a recall on several Main Switches - Main Contractor stated he could not attend so MK Passed it onto myself!

Look i don't need to explain myself to you - yes I should of taken a picture and maybe you would have seen.

I have a very good reputation in this end of the woods - Working for several very large names including the ones mentioned in this thread and many others.


I only posted this as a good conversation - yes I should of said more in the OP

Lets put this thread to lay because at the moment Dillb you are only obsessed in having a bitch like always!

END OF!

Ha ha, I remember a very similar thread about a fire in a recently installed CU, and the same thing was said then, "Lets put this thread to lay ",
lol
Nicholas is that you ? lol
 
Last edited:
Ha ha, I remember a very similar thread about a fire in a recently installed CU, and the same thing was said then, "Lets put this thread to lay ",
lol
Nicholas is that you ? lol

That's not the only similarity to Nic's style of writing. Plenty in this thread and a couple if others he has started.
 
Lol who changed his name to spazz?

I have no idea lol

Another thing not apparent from that old thread, was that Trev was winding him up about the local officials at his (Nicholas's) Fire HQ, he had looked up their names on the net lol, we knew, but watched him bite.

A couple of posts appear to be missing/moderated.

It was funny at the time to watch him try and squirm his way out.

I actually quite liked Nicholas, as he meant well, just he was a bit Walter Mitty, and he had a bit of a thing for RCDs and Part P/ESC.
 
Last edited:
Are all electrical contractors from Pembrokshire full of it?

I remember your identical twin brother Nicholas Owen also being from that neck of the woods.

This is on the home page of his website "Our Basingstoke Office covers the East of England including London and Leeds." I always thought that Leeds was up north!
 
leeds was up north until recently, when glenn hammered in a huge earth rod, so huge that it altered the centre of gravity of the earth and now leeds is sub-tropical. all this because he wanted to wear his new burmuda shorts for work.
 

Reply to Non Registered Spark wiring NewBuild in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I decided not to tackle installing an extractor fan in our bathroom myself but to get in a professional. I checked with Building Control and they...
Replies
7
Views
1K
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
649
Had a lovely conversation/argument with building control this morning, the scenario is this, Completed job (4 flat rewire) EIC’s sent to client as...
Replies
12
Views
3K
What certification do I need when replacing a consumer unit ? Here are the details. I am semi retired (electrician) and work for a company as...
Replies
48
Views
8K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock