Discuss NOT SEEN THIS BEFORE. ASSUME PME??? in the UK Electrical Forum area at ElectriciansForums.net

telectrix

-
Mentor
Esteemed
Arms
Reaction score
67,273
as title.cable tapped into N, disappears into the ground. assume to a rod.

009.jpg
 
Presumably now at least PNB!
That "crimp" can't have been left like that (is one of the neutral strands snapped?); it does look like a cable could have been connected to the next joint along the cable at some point, maybe this was a method of restoring back to how it was.
Not sure this is an approved method of applying TNCS for an incoming supply.
 
Presumably now at least PNB!
That "crimp" can't have been left like that (is one of the neutral strands snapped?); it does look like a cable could have been connected to the next joint along the cable at some point, maybe this was a method of restoring back to how it was.
Not sure this is an approved method of applying TNCS for an incoming supply.
well it's a DNO bodge then. this house is the last of 6 on the run. . none of the others have antything like it.
 
back there today. will measure Ze, PSCC, and PEFC.
 
If it's the last house of the run, it will be 16mm hard drawn copper down to an earth rod as per DNO PME regs. Should have a PME label attached.
 

Reply to NOT SEEN THIS BEFORE. ASSUME PME??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
555
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
645
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
584
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
9
Views
441

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock