Good morning all

Is there any reg to say about drilling cables into joists instead of notching?

I have been an electrician for 12 years now and have always drilled out timbers, we are starting a HUGGGGGGGGGGE rewire with long runs. It would save a lot of time i think to notch the top of the timbers and use a protective metal plate to go over after the install

Thoughts?
 
Notching is still acceptable, I’ve pulled this from the OSG for you.
image.jpg
 
The strength of a rectangular beam loaded in the vertical direction depends on the second moment of inertia I. Where I= B*D(cubed)/12 . Where B is the width of beam and D is the depth.
You need to know the exact dimensions but as an example: for a six-inch-deep beam with a one-inch- deep notch, the beam becomes effectively five inches deep. So, the original D(cubed) was 216 and the modified D(cubed) becomes 125. The strength is now 125/216 or 58% of the original.
For changes in stress levels, other factors such as distance from supports, are relevant.

For interest:
If you halve the width of a beam you reduce its strength by a factor of two.
If you halve the depth of a beam you reduce its strength by a factor of eight.
If you halve both width and depth you reduce its strength by a factor of sixteen.
 
The strength of a rectangular beam loaded in the vertical direction depends on the second moment of inertia I. Where I= B*D(cubed)/12 . Where B is the width of beam and D is the depth.
You need to know the exact dimensions but as an example: for a six-inch-deep beam with a one-inch- deep notch, the beam becomes effectively five inches deep. So, the original D(cubed) was 216 and the modified D(cubed) becomes 125. The strength is now 125/216 or 58% of the original.
For changes in stress levels, other factors such as distance from supports, are relevant.

For interest:
If you halve the width of a beam you reduce its strength by a factor of two.
If you halve the depth of a beam you reduce its strength by a factor of eight.
If you halve both width and depth you reduce its strength by a factor of sixteen.
Plumbers are exempt though! ;)
 
Personally I don’t notch beams. Over the years I’ve been unlucky enough to damage a few cables installed this method.

Someone has designed the beam to meet a load and as @ELECNEWT has mentioned notching will not help. Also, any top protection plate needs to be properly effective as any future damages or injury caused by penetrating the plate will be down to the installer, in my view. I haven’t seen a protection plate I trust so if I work on a circuit that has notching I re do it. This one was yesterday. Probably why I’m poor.

7C5E18AB-8CB9-4E7C-994A-81DC36140394.jpeg
 
if. like me, you've worked on a load of terraced houses, top of stairs you often find a 3ft square "landing" between fron and rear bedrooms. the floor joists are 4" x 2" and as such drilling centre of joist ,cables will be <50mm from both surfaces. here, the only compliant option is to notch and plate.
[automerge]1596266761[/automerge]
Plumbers are exempt though! ;)
yes but plumbers do actually test the strength of the joist when notching out with an axe.
 
Last edited:
Notching sounds good, if joist are close together,nothing worst pulling cables through tight joists,especially several,watch the shaffing?
 

Reply to Notching timbers instead of drilling.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
20
Views
2K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
718
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock