Just put a new cu in started testing .so here it goes start doing rfc line 0.33 nn 0.32 cpc 0.55
Ins all good now this a split load
Dis the cpc what i was working on and now showing earths in and are out so theor is no parallall paths has far that i can see the main earth is out but showing earths all water and gas have been disconnected
 
Another possibility is the existing rings have been extended to enable more outlets, the lines and neutrals are incorporated into the existing ring but not the cpcs not so they have effectively become a figure of eight.
 
Any metal stud work in the property? a lot of other trades use the metal stuff rather than timber these days. often find boxes joined to the metal studwork.
Also any chance of damp or moisture in the walls between back boxes if they have the cpc in them?
Came across something similar when I was still at college and just started working. property had a bad damp problem that once sorted out resolved the irregular readings??
 
This is where Wander Lead is so so useful :)

IMG_1051.JPG


Gratuitous reposting of Wanda Ventham
 
All sockets have been disconneted except for the skts up stairs had every skt off dis the met earth still showing earths thier. no cable touching any pipe work up stairs had most of the floors up .
 
Check voltage from line ,to earth you socket tester may be giving you a false indication of a earth , by the way is it a good idea to remove the cpc then make the circuit live ? , and what is the issue here , you have a parallel earth path? Ps now i know my spelling is bad but maybe you should take off your space gloves so you may have a better chance of hitting the correct letters ☺
 
I'm confused here as well. All cpc's and earthing has been disconnected from the Consumer Unit, and you have now energised the circuits?

Surely not?
 
Why have you energised a circuit with no cpc's connected?
how discovered
the earth was not in play when doing a r1+r2 to see if I had the wright circuit by leaving off the earths when putting the socket and see tester in to indicate that a had that circuit .and then it showed me earths present when the cpc earths not connected .
 
I still don't see what you are hoping to find or achieve here. It could be supplementary bonding, it could be metal dual boxes. It's a parallel path somewhere. If I was the customer I wouldn't like to be paying for all this unneeded work.
 

Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
741
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
838
DIY at my friends house, his pull cord stopped working for bathroom light, so i went over and the wires that are coming out the roof was 3 wires...
Replies
14
Views
2K
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
2K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
955

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top