Discuss One question regarding filling the PIR. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nazoom

I am still training to become qualified. I have the following question regrading filling the Schedule of Inspection for Periodic inspection report.

When do we use N/A and when do we use N/V? I am slightly unsure when may be some examples will help.

Many Thanks
 
N/A means that its not applicable ie if the are no selv or pelv

N/V should not really be used on the Schedule of Inspection as the tester should be checking and ticking, N/A or failing the listed items

(N/V i suppose could be used if there was some agreed limitations listed ie the client does not want downlights taken down to check if they are fire rated in case the ceiling gets damaged)
 
Last edited by a moderator:
I am still training to become qualified. I have the following question regrading filling the Schedule of Inspection for Periodic inspection report.

When do we use N/A and when do we use N/V? I am slightly unsure when may be some examples will help.

Many Thanks

You should be completing the new Electrical Installation Condition Report now, not the old PIR.

Cheers...........Howard

PS,

N/V = Not Verified
N/A = Not Applicable
 
LIM is for a limitation to the inspection and test, this is agreed with the tester and the client. If you cant isolate part of the install, then you have a LIMitation.

Not Verified means that you could not verify a part of the installation, such as, you got continuity on a bonding conductor between the earth terminal and a pipe, but you couldnt verify that it was connected to the water pipe, cos you couldnt see it, some knob had hidden it behind a cupboard or similar. You got a reading, but couldnt verify it was connected properly.

Cheers.........Howard
 
LIM is for a limitation to the inspection and test, this is agreed with the tester and the client. If you cant isolate part of the install, then you have a LIMitation.

Not Verified means that you could not verify a part of the installation, such as, you got continuity on a bonding conductor between the earth terminal and a pipe, but you couldnt verify that it was connected to the water pipe, cos you couldnt see it, some knob had hidden it behind a cupboard or similar. You got a reading, but couldnt verify it was connected properly.

Cheers.........Howard

If you can't isolate all or part of the install it should be noted in the "limitations", then it is an N/V ie it can't be verified as it is a limitation. Then again........ Cheers Billy
 
So is it safe to say that it is unlikely we use N/V or LIM for Periodic Reporting?

Thanks.

the other way round nazoom
on an initial inspection of new wiring there shouldnt be any n/v or lim's as you should have confirmed all requirements as you go along
but on a periodic inspection limitations are common due to access etc.
 
N/A.... there's no way you're having sex tonight.

N/V.... i might if you're nice to me

LIM.... OK then, but don't you dare get me pregnant.
 
I never use N/V, I always put LIM and fill in the agreed or operational area of the test sheet with why its a LIM.

A clasic one is the Main service fuse I would put LIM and in the operational limitation box put unable to varify size and rateing of main service fuse.The tick sheet on the click NIC software doesnt even have N/V as an option.
 

Reply to One question regarding filling the PIR. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
846
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
794
I was surfing through one of the electrical training groups on Facebook yesterday and came across this question from an AM2 prep course: There...
Replies
7
Views
991
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
799

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock