Discuss Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?

1. I did not open the head - I was not the photographer.
2. Yes I did. To avoid any chance of multiple earth paths.
 
I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.

So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.
 
IMG_2950.GIF

I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.

So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.
The neutral and cpc are not combined in the service head and are separate split like the picture
 
View attachment 37591

The neutral and cpc are not combined in the service head and are separate split like the picture

Thanks for the picture - that looks very much like the configuration in the image I originally posted. Just to clarify is the consensus still that this is TN-S?

This would align with the observation that the PEFC and PSSC are different.

Thanks again for very helpful insights from the forum.
 
I would go for TN-C-S.
If you look carefully at incoming supply, the concentric cable has only 2 conductors. The centre line conductor and outer stranded neutral. Part of the stranded neutral has been seperated and used to feed the earth terminal. (Effectively creating a link between them) the remaining strands have then been painted black to form the neutral conductor.

So to my eyesight, which is not what it was, it's combined in the service head, therefore TN-C-S.

Time to go to spec savers I think, there are clearly three separate conductors there!
 

Reply to Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes...
Replies
2
Views
768
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
795
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock