Hi,
I am the wife of an electrician feeling absolutely gutted. We have had a complaint from a customer who is seeking a £500 refund for a consumer unit change that my husband undertook for her. I joined here in the hope other electrician's could shed some light on what's happened as I have no clue what consumer unit wiring should look like. I can't confront my husband over this at the moment as his mum is dying and I don't want to add to his stress so I am trying to figure it out myself. My husband has been an electrician 30 years. He is a part P domestic installer, Niceic registered and 18th edition updated last year. We have hundreds of happy customers since he went self employed 2 years ago. I do all his books and customer communication etc and he has never had a complaint up until now.
So basically he started on a job where there were other tradesmen present , including another electrician who was retired .My husband did lots of various electrical jobs for this lady who paid us promptly after each installation and was very happy with his work ,even leaving a good review on Google ads for him ..but then something happened, roughly 4 days after he replaced her consumer unit she called us to say it keeps tripping. He went back over there to try to figure out what was happening and spent half the day there. He came back very frustrated saying he couldn't figure it out. There were 5 other tradesmen there,( the place is being renovated) including this other electrician who apparently couldn't understand why it was tripping either. My husband said he ended up ripping all the wires out in order to get to the bottom of it. ..It ended with my husband telling the customer he was completely stumped and that she should get a second opinion.... I then get sent these pictures a week later from the customer of what she says is my husband's work. I am baffled! To me it looks a mess but I realise she probably took this photo AFTER he dissected it for the tripping fault??
Please can anyone of you guys offer me some opinions here as I'm really distressed by this.
Fivehead DB (001).jpg
 
Notwithstanding the messy wires, what is tripping, an individual MCB or one of the RCB's, why is one of the MCB's taped over and another off, or are these things tripping?

The far left neutral bar has black wires into it, this would tend to indicate an old circuit, I would start there.
 
It is untidy. Leaving the customer to get a second opinion was probably his biggest mistake. I'd say he'd best ask permission to return and sort the problem out himself. I realise his delicate position at the moment, so would a colleague be able to do this on his behalf?
There are a couple of other small issues, but not worth mentioning as you are not electrically trained.
 
Being messy doesn’t explain the tripping.

It’s a case of going through each circuit, disconnecting the live and neutral from the board and testing.

your husband maybe is just overthinking things when he has other things to deal with.
a couple days away, and return to the job with fresh eyes, it might just pop up at him.
 
i always take photos of how i left an install, esp. consumer units. that job as per your photo is a mess. without a photo of how your husband left it, we can't tell who's to blame.
Thank you for replying. Yes that is definitely a very good idea. It's the messy wiring I think she is judging the most. Can you tell me please does this wiring look standard for a consumer unit replacement where the wires are existing? I have seen pics online of new installation's where the wires are all neat and straight but is this unfair to compare against? Or am I clutching at straws??
 
This is one I fitted onto existing wiring. To be honest your husbands isn't great and we wouldn't tolerate work to that standard.
,Yes, it isn't great, but to be fair to the OP, his CU appears to have a LOT more wires than yours, and on a CU change, the existing wiring doesn't always come from the ideal direction, or have sufficient length to make the job as neat as you'd like.
The OP's pic. looks like it may have been neater, but the cpcs, which most would connect in place first, look like they may have been disconnected from the bar for testing purposes, and unthreaded through the lives and neutrals.
 
It would make it 10 times easier to fault find if the boards cabling was sorted and easy access was created.
agree with @westward10 i wouldn’t accept the board finish as it is shown in photo.

if the tripping has started 4 days after the installation something must have happened to make this occur. But your husband needs to return to job to prove this.

if it was me I would return and find fault and rectify it. If the fault was not caused by my work I would charge for the return visit, however in this situation I don’t think I would charging extra due to quality of work.

sorry if I’m a bit brutally honest, but best you get the truth.
 
I started to feel very uneasy when reading there is other work taking place. It is possible your husband is stressed and has assumed that his testing on the CU installation is still valid, but in fact stuff has been changed after that either deliberately as accessories are replaced, or accidentally if a cable is damaged by other work.

The board looks untidy, as others have already said that might have been made far worse by some fault-finding already. I expect the customer's real issue is not believing it can be fixed properly. That is something your husband will have to address or give up and refund.

Really he needs to go back with plenty of time and systematically check all circuits, assuming nothing, and checking for the usual suspects for mysterious trips:
  • N-E faults (should be apparent on insulation testing)
  • A "borrowed" neutral on up/down light circuits
  • Faulty RCD (trip time & ramp testing should eliminate that)
  • Faulty appliances being used (washing machines with water leaks, etc, but checking leakage in-use after all of the above should show this)
It needs a methodical approach, and not to have others monkeying with the electrics in the background as they do their work though. Also an opportunity to leave the board looking much neater!
 
Does your husband have any notes of test results after he finished the board change, and did he get as far as writing out a certificate? Or have the family circumstances meant it hasn't been tested?
The reason I ask is that if one of the other trades has damaged something somewhere since (which is perfectly possible) then a fresh round of dead-tests will a) quickly show where the issue is and b) prove it happened after he left.
Either way the quickest way from here is to test and build up from scratch again as others have said.
 
If it started tripping 4 days later and there are other trades on site then they have possibly damaged something? Its an occurrence which is all too common although the other trades will of course deny doing anything.
 
To be honest it does look a mess and like others have already stated it needs to be tidied up.
To be fair with all the other trades around, your husband was probably under stress or perhaps he has been stressed for quite a while and you may not have noticed, sometimes the ones closest don't see the signs of stress. He may have taken his eye of the ball so to speak.
Obviously the fault needs to rectified and perhaps it was some occurance after your husand's work that caused it, I doubt anyone will owned up to that so it's a case of returning and investigating the installation or passing it on to a trusted friend who could maybe assist in putting it right.
Personally speaking I would return and carry out inspection/testing of the installation and try to win this customer back on side, one unhappy customer can make your business go downhill fast if they start to spread tales of your workmanship.

Under the circumstances though, it may be better if your husband is under a great strain at present and to save yourself getting really stressed about the situation to refund or someone you know and trust to act on your behalf to put matters right.
 
To be fair to all concerned I think a refund is in order. This is clearly a difficult time for you both and sometimes it's hard to see the woods for the trees. I would say that if the price was for the consumer unit supply and fit then the customer should pay for the materials and not the labour. So in the first instance in your shoes I would suggest this to the customer. As to the fault, no doubt someone will come along and find it and that will cost xyz, I would offer to cover the cost of this for the customer. This may amount to more than £500 refund. Everything is negotiable and of course you would wish to at least attain an equitable solution for all parties. So either refund the £500 or take the alternative route as above. Of course it may be as suggested above, one of the trades has unwittingly drilled a cable or something and if this is shown to be the case then reserve the right to insist the guilty party (so to speak) pays for the rectification of the fault. Believe me, I think most sparks here have had a bad day with things like this and these things do happen try not to take it too hard.
 
To be fair to the original electrician, do you actually believe that he would have left the CU in that condition, I think someone has been playing around with it since he did the original installation and that is what I would be saying to the client, together with "there were no faults on any circuit when I left site on (insert date important as it establish's a time line of first visit) therefore I would suggest that some damage has been done to the installation since I completed my work on the first visit, I would be only to pleased to return to try and solve this problem, my hour rate is £....
 

Reply to Opinion on these pics please in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock