N

Nicebloke

If running power to an outbuilding (usually a garage at the bottom of someones garden), I normally run it from the non RCD side of the C/U in the house and then put a 2 way RCD protected C/U in the garage. I was however, told that I can no longer do this as it must be connected to an RCD in the house C/U. I was also told that any outbuilding more than 20 metres away from a house must have it's own TT system?
 
If running power to an outbuilding (usually a garage at the bottom of someones garden), I normally run it from the non RCD side of the C/U in the house and then put a 2 way RCD protected C/U in the garage. I was however, told that I can no longer do this as it must be connected to an RCD in the house C/U. I was also told that any outbuilding more than 20 metres away from a house must have it's own TT system?
where did you hear this?
 
Surely yours is the best method, as long as the cable has physical protection (i.e. not triggering the cables in walls reg). Having RCD in series is difficult to discriminate and the longer the run the more impact it has. A lamp blows in building2 at night and trips a board in building1 a 100m away creating an unnecessary hazard, imho.
Edit : and the reverse, a problem in building1 takes out RCD covering building2
 
I am with Stroma. With regards an outbuilding requiring its own TT system if it's more than 20 metres from the house, I can't see where he got this from?
 
I am with Stroma. With regards an outbuilding requiring its own TT system if it's more than 20 metres from the house, I can't see where he got this from?
out of a chinese christmas cracker, i'd assume. what a load of bollox.
 
While there are arguments to support that thinking, it is only one way of doing it, there is guidance to download called Exporting PME. If I put an RCD at the house I personally would only use that for the cable protection supplying the garage and do a TT at the garage. I understand the DNO do not like exporting PME too far from the origin as it may defeat their PME. But the above is not set in stone, there are other approaches.
Exporting Pme - http://www.electriciansforums.co.uk/resources/exporting-pme.101/
 
This is where it all goes wrong when you have different bodies giving different opinions, and within those bodies you have people who seem to have their own misguided opinions. One body, one set of rules is what it should have been.
 
Its all down to economics
A ridiculous attempt at regulating domestic electrics in a market driven arena has resulted in Tom Dick and especially Harry becoming overnight pretend electricians signing up to the least costly player

The least costly player has no historic base or experience of the industry,it has had to recruit its team to meet the lowest cost demand
That team will also include inexperienced assessors gleamed from a pool of sparks where the skill level has been decimated since the introduction of that hatchet of the trade of electrician,Part P of the building regs
 
Its all down to economics
A ridiculous attempt at regulating domestic electrics in a market driven arena has resulted in Tom Dick and especially Harry becoming overnight pretend electricians signing up to the least costly player

The least costly player has no historic base or experience of the industry,it has had to recruit its team to meet the lowest cost demand
That team will also include inexperienced assessors gleamed from a pool of sparks where the skill level has been decimated since the introduction of that hatchet of the trade of electrician,Part P of the building regs

As a contrary opinion to that I can say that my stroma assessor was a time served electrician with many years experience and seemed to be a very knowledgeable fella.
 
As a contrary opinion to that I can say that my stroma assessor was a time served electrician with many years experience and seemed to be a very knowledgeable fella.

Andy,I don't doubt for a moment that they have assessors who are at the top of their game

quote
That team will also include inexperienced assessors
 
It does seem to vary between assesors doesn't it. My last assesor was great & really did know his stuff, but the one before that started to get all confused (I saw it on his face) when I was explaining why I used an s type rcd to replace the main switch in an all rcbo board on a TT supply.
 
If running power to an outbuilding (usually a garage at the bottom of someones garden), I normally run it from the non RCD side of the C/U in the house and then put a 2 way RCD protected C/U in the garage. I was however, told that I can no longer do this as it must be connected to an RCD in the house C/U. I was also told that any outbuilding more than 20 metres away from a house must have it's own TT system?

OP, I would consider emailing your scheme's technical support, and seek clarification on this matter. I find emailing gets a more defined and considered response, than by speaking to an individual.

I'm with Elecsa, and quite often I've read & heard conflicting guidance on issues (nothing as profound as this mind), when watching their web broadcasts, and what is written in their 'Connections' publications. The last one was about upgrading bonding, it used to be it was okay to leave as is, if there was no sign of thermal damage. Then the mag' said, no it must be upgraded, then the dynamic duo said, it was ok to leave etc. :rolleyes:
 
OP, I would consider emailing your scheme's technical support, and seek clarification on this matter. I find emailing gets a more defined and considered response, than by speaking to an individual.

I'm with Elecsa, and quite often I've read & heard conflicting guidance on issues (nothing as profound as this mind), when watching their web broadcasts, and what is written in their 'Connections' publications. The last one was about upgrading bonding, it used to be it was okay to leave as is, if there was no sign of thermal damage. Then the mag' said, no it must be upgraded, then the dynamic duo said, it was ok to leave etc. :rolleyes:
Dynamic Duo One has to be TC who is the other?
 
It does seem to vary between assesors doesn't it. My last assesor was great & really did know his stuff, but the one before that started to get all confused (I saw it on his face) when I was explaining why I used an s type rcd to replace the main switch in an all rcbo board on a TT supply.
That's a bit concerning.
 
^^ so what did you say when he made his "claim"?

I explained why I did it the way I do, and he said it still had to be on an RCD in the house C/U. With regards a TT system being required if an outbuilding was more than 20 metres away from the house, I just said that I honestly wasn't aware of that.

I could have asked him to show both the above in the regs, but I just wanted to pass the assessment (which I did), and I admit that I did slightly doubt myself that he must be right as he seemed so confident.

I have had assessors before from another body who knew their stuff, so as already suggested some are clearly better than others and it's the luck of the draw.
 
I explained why I did it the way I do, and he said it still had to be on an RCD in the house C/U. With regards a TT system being required if an outbuilding was more than 20 metres away from the house, I just said that I honestly wasn't aware of that.

I could have asked him to show both the above in the regs, but I just wanted to pass the assessment (which I did), and I admit that I did slightly doubt myself that he must be right as he seemed so confident.

I have had assessors before from another body who knew their stuff, so as already suggested some are clearly better than others and it's the luck of the draw.

As suggested, email and get clarification.
 
Because some single pole rcbo's will only disconnect the L leaving the N connected in a fault, so if you had a N - E fault the rcbo would trip, but the N - E fault would still be present and current will be flowing. the upfront s type would detect this and trip. Kind of like a backup really if that makes sense.
 
Because some single pole rcbo's will only disconnect the L leaving the N connected in a fault, so if you had a N - E fault the rcbo would trip, but the N - E fault would still be present and current will be flowing. the upfront s type would detect this and trip. Kind of like a backup really if that makes sense.

Yeah I get what you mean but don't see why you installed RCBO's. This is one time a dual RCD board would have been better. This way at least half the circuits would stay on in the event of a neutral earth fault where as in the event of a neutral earth fault with that setup your loose the lot. You may as well of installed a 30mA upfront RCD and used circuit breakers...Would of been cheaper and still would of had the same affect. If I was your assessor you would have got a bemused look from me as well :p:D
 
Yeah I get what you mean but don't see why you installed RCBO's. This is one time a dual RCD board would have been better. This way at least half the circuits would stay on in the event of a neutral earth fault where as in the event of a neutral earth fault with that setup your loose the lot. You may as well of installed a 30mA upfront RCD and used circuit breakers...Would of been cheaper and still would of had the same affect. If I was your assessor you would have got a bemused look from me as well :p:D

I said I would get all confused again.

Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
 

Reply to Outbuilding on non RCD side of C/U? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So as the title says can I use a mcb as the main switch. Basically to keep it short I’ve took a 25mm sub main to power an outbuilding. Mains...
Replies
11
Views
3K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
916
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock