Discuss Outbuilding on non RCD side of C/U? in the UK Electrical Forum area at ElectriciansForums.net
I said I would get all confused again.
Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
I said I would get all confused again.
Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
That's why I use RCBO's on TT. Don't personally like the idea of unprotected single insulated conductors supplying the 30mA RCD's. I know we still have the busbar and tails to think about, but the busbar is solidly in place and the chances of that falling out is slim and if the tails are secured well so are they. But leesparkykent does have a good point about loosing the whole board in a N-E fault.
BORING.BORING.The OSG gives guidance on TT supplies and use of RCBO's & RCD. Suitable use of glands would mitigate the tails shorting against the metal enclosure on entry. The issue with using RCD in such an enclosure, is the single insulated cable supplying each RCD, which may be damaged or pinched, and shorting with the metal enclosure. Using an up front S Type would provide fault protection in this case.
The issue with using SP RCBO's and upfront S Type, is in the case of a neutral-earth fault, is the S Type would eventually trip, but would then isolate the entire installation. Using dual RCD's, the same fault would only isolatate one half of the installation. Some guidance I received from my scheme Elecsa;
Good morning and thank you for your enquiry.
In regards To a TT and isolation of circuits regulation 537.2.1.1 must be taken into consideration. This regulation requires every circuit to be capable of being isolated from each of the supply conductors. (except in a TN-S or TNC-S)
This can be done various ways and it is permissible to isolate more than one circuit from a single device (GN2 section 4.3).
In the situation you describe with RCBO’s a double pole device will meet this requirement.
For further guidance refer to Guidance Notes 2 Isolation and Switching section 4 and the OSG as advised.
The diagram in the OSG that you mention (3.6.3.(iii)) is just one acceptable arrangement of RCD’s in a TT system. Other suitable arrangements are shown in 3.6.3.(ii) – (v).
It may be worth reading sections 2.2.5 & 2.2.6 (pages 20 & 21) in the OSG and also sections 3.6.1 – 3.6.3 (pages 30 – 32) and also section 3.6.3.4 on page 35 of the OSG.
It may also be worth reading regulation 531.4.1 & also regulation 537.1.2.
Some sections of BS7671 state the use of DP RCD’s, such as installations that fall under sections 705 & 708.
CAN'T KEEP MY EYES ON THE CIRCLING SKIES.
Yeah but the point I was making was the RCBO and upfront combo in the event of a neutral earth fault they would ending up loosing the lot as the up front RCD would still trip as the Wylex RCBO's are solid neutral. So it would be no different having a 30mA up front as you they would still loose the lot. That's why with TT its really RCBO's with no up front RCD or a dual RCD board with upfront RCD.I said I would get all confused again.
Surely even a dual RCD A3 CU, will require a 100mA S Type RCD (as main switch or upfront) on an installation forming part of a TT supply, as the S Type will provide fault protection for the single insulated conductors supplying the 30mA RCD's?
Yeah but the point I was making was the RCBO and upfront combo in the event of a neutral earth fault they would ending up loosing the lot as the up front RCD would still trip as the Wylex RCBO's are solid neutral. So it would be no different having a 30mA up front as you they would still loose the lot. That's why with TT its really RCBO's with no up front RCD or a dual RCD board with upfront RCD.
I'm going to start using dual RCD boards with 100mA s type upfront or DP RCBO's from now on on TT. Thanks @Leesparkykent for that, we learn something every day